    Bluebox Water Cooled Screw Chiller_Pressure Relief Valve Issue



    Dear All,

    We are facing one strange problem of opening of Pressure Relief Valve(PRV) at condenser before the HP Alarm (through 1 HP Transducer and 2 HP Switch) is activated. Initially we thought the issue is with the valve, but later on we found strangely that at Hot Gas Discharge line, Discharge pressure is under HP limit whereas at liquid line before Drier, the pressure has increased to whopping 9 bars above Discharge Pressure measured at Compressor Outlet!! We found the reason why PRV opened before HP, but we are still not able to understand the increase in Pressure. Its R134A based system.
    I would like to inform you that this Chiller is operational from past 3 years and working fine till now.

    Any support will be great help!!

    Regards,
    Siddhant
    New Delhi, India



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Bluebox Water Cooled Screw Chiller_Pressure Relief Valve Issue

    Sbkvelocity,
    Can you confirm with a known calibrated gauge that discharge pressure transducer is
    reading correctly.
    Measure both points at same time, in off & running condition.
    Nohing is impossible, but sounds unlikely.

  3. #3
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Bluebox Water Cooled Screw Chiller_Pressure Relief Valve Issue

    Interesting....This thing economized? Any oil cooling arrangement?

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Bluebox Water Cooled Screw Chiller_Pressure Relief Valve Issue

    when it happen ?
    is it in starting time or in running time.
    what is your setting pressure for HP and PRV. and ambient temp.
    do you have small valve in line of gauges?
    are they work correctly?

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Bluebox Water Cooled Screw Chiller_Pressure Relief Valve Issue

    any check valves anywhere in system creating liquid lock, and hydraulicing liquid line.