Results 1 to 5 of 5
  1. #1
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    searle ks70 evaporator bearers



    Does anyone know what the amperage draw should be for the evaporators bearing in mind there is two wired in series ,they are 110volt wired in series with a 240volt supply.
    Last edited by cadwaladr; 21-07-2014 at 03:30 AM.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: searle ks70 evaporator bearers

    Each fan the amps you find on the nameplate and if 2 in serie, 2 x Amps as found on nameplate
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: searle ks70 evaporator bearers

    Sorry the post should have said evaporator heaters

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: searle ks70 evaporator bearers

    Hi Cad.
    Check out the attached.
    Grizzly

  5. #5
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: searle ks70 evaporator bearers

    Got it sorted today! Found out that the heaters should take approx 9 amps each and should be wired in parrell contrary to advice given to me by a colleague,all up and running defrosting fine thanks for the help guys,now the invoice can be sent!