    Toyo Split system external fan.



    Hi Group

    I am new to the forum. I have a Toyo split air con system not an inverter unit.
    I am a beginner working on air con units usually I do gas and oil boilers.

    The outdoor unit fan is not running but the compressor does until
    it becomes too hot.

    I have traced this back to the solenoid on the circuit board not supplying
    240volts. If I supply the 240volts it works fine.

    A quick question is does the fan usually get switched by some thermostat in the system that might be faulty that I haven't seen or should
    it simply run all the time that the unit is on for cooling?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Toyo Split system external fan.

    solonoid?- do you mean relay?- test ur gettin 240 on the other side of the relay- you can flip the cover off omron pcb relays to see the contacts, some fans are 2 speed- check for wiring diagram on the lil cover plate on the electrics or indoor unit

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Toyo Split system external fan.

    Are you F-Gas qualified? ^what monkey said, though it might have a solid state relay which you won't be able to see the contacts on.
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Toyo Split system external fan.

    You could temporarily wire the fan live onto the output side of the compressor contactor/relay through a small inline fuse to see if it runs OK. This will bring the fan on when the compressor runs so you shouldn't get a high pressure trip.

    Remember I said 'Temporary' fix :-)

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Toyo Split system external fan.

    on a toyo unit john- more clockwork than an imi hilo unit! haha

  6. #6
    Join Date
    Aug 2014
    Location
    Singapore
    Age
    39
    Posts
    1
    Rep Power
    0

    Re: Toyo Split system external fan.

    Hi there. I'm new here. I have my problem in my Toyo split air con, I guess it's Electrical Wiring is affected. I decided to find a better to fix it. Do you have any recommendation? If you have, kindly update me. Thanks!
    Last edited by frank; 04-08-2014 at 09:51 PM.

  7. #7
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    624
    Rep Power
    16

    Re: Toyo Split system external fan.

    Quote Originally Posted by ref567 View Post
    Hi there. I'm new here. I have my problem in my Toyo split air con, I guess it's Electrical Wiring is affected. I decided to find a better to fix it. Do you have any recommendation? If you have, kindly update me. Thanks!
    make a new thread man !!!

  8. #8
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    624
    Rep Power
    16

    Re: Toyo Split system external fan.

    as guys above said


    the fan relay in the indoor unit may be damaged
    or the indoor pipe sensor which measure the temp then control the fan work in heating mode
    so the the sensor may be fault
    Last edited by kefah; 07-08-2014 at 11:33 AM.