    Daikin VRV III Heat Recovery - LC error fault code



    Hi,

    Anyone familiar with the LC error on Daikin VRV outdoor unit?

    I'm servicing a Daikin model REYQ12P9Y1B, I've replaced all the boards, tested fan motor and inverter compressor. All connections are good between boards.

    I don't know what else to do. Is there any procedure I'm missing? Hard reset?

    I've heard there's a rewiring mode but I don't know how to activate it...

    Any pointers would be appreciated!

    Thank you

    Vitor



  2. #2
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    48
    Posts
    184
    Rep Power
    20

    Re: Daikin VRV III Heat Recovery - LC error fault code

    Which PC boards did you replace? LC is communication error between inverter PC board and the outdoor control PC board. Chech the following:
    1. Fan inverter PC boards
    2. Compressor inverter PC board
    3. All your inverter PC board wiring
    4. Compressor Short circuiting
    5. Fan short circuiting
    6. Faulty noise filter
    7. Faulty PC board

    hope this will help.

  3. #3
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    48
    Posts
    184
    Rep Power
    20

    Re: Daikin VRV III Heat Recovery - LC error fault code

    With daikin its just a test mode which you run for the master PCB to pick up and configure the rest of the system components. Daikin runs training courses which cover how to run such operations. have you been to one of these courses? You can access the information on the procedure of doing this in the service manual of the unit. If you dont have it let me know I will send it to you. pkatete@gmail.com

  4. #4
    Join Date
    May 2011
    Location
    Россия
    Age
    43
    Posts
    18
    Rep Power
    0

    Re: Daikin VRV III Heat Recovery - LC error fault code

    VitorFC, Take a picture of all the boards and wires. Maybe someone stole the connecting cable.

  5. #5
    Join Date
    Aug 2013
    Location
    greece
    Posts
    6
    Rep Power
    0

    Re: Daikin VRV III Heat Recovery - LC error fault code

    LC
    80% inverter compressor
    20% inverter PCB

    definitely in VRVIII you MUST replace them together

    here is the troubleshooting
    https://app.box.com/s/59bs5i1rib1iopgvlpah

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV III Heat Recovery - LC error fault code

    the rewire mode your referring to is the wiring check function- this needs to be performed if youve swapped the main pcb
    check for green flashing led's on each pcb-prooves comms, also check the 3 wire comms cables as the can vibrate out their connections on the pcb, also ensure your mains supply is correct, no loose connections or water ingress

  7. #7
    Join Date
    Jul 2014
    Location
    Portugal
    Age
    42
    Posts
    2
    Rep Power
    0

    Re: Daikin VRV III Heat Recovery - LC error fault code

    @PRESS; @Onsyi; @martinoff; @install monkey

    Thank you for all your help.

    Now I feel kinda silly but I found that the fan inverter boards are different for MF1 and MF2, they are exactly the same but have different part-numbers.

    I was using 2 MF2 inverter boards.

    So the malfunction was a fan motor (MF1) and a busted MF1 inverter board.

    Well, I still had some difficulty setting the system, but after some fiddling it started working.

    Thanks again