    High pressure Climaveneta FOCS FC 4822



    Hi , we have a chiller climaveneta FOCS FC 4822 with 2 circuit ,R 134 , i have this problem; High presure alarm 211 , i reset from mechanical presure switch , and i restart the compressor (bitzer CSH ....) The compreosr start but after ,not more ,than 10 second stop with alarm 211 (high presure) , 18 bar measured before dry filter , and 7 bar after the thermostatic expansion valve PHT/Q 125 (026H1164) from Danfoss .
    Is possible that this valve to not open ?
    We dont change the cartridge filter yet , it is possible to be from this one?



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: High pressure Climaveneta FOCS FC 4822

    Hmm,

    The pressure you need to be looking at is the discharge from the compressor.

    Unlikely to be the TEV, if that don't open the system will more likely cut out on low pressure.

    If the discharge pressure is only 18 Bar, it would be worth checking at what pressure the HP switch cuts out and check it against what pressure it should cut out at.


  3. #3
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: High pressure Climaveneta FOCS FC 4822

    hi what refrigerant are you using,if its r134a then 18 bar is high
    if its r407c then it can run at 20 bar easily, check pressure switches

  4. #4
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: High pressure Climaveneta FOCS FC 4822

    together with advise from Ghaz and Viking you can also check your condenser fans operation. that chiller has two compressors and two seperate refrigerant circuits and is this happening in just one circuit or both? condenser fouling can also be factor causing this. it is highly unlikely that this can be caused by blockages in the liquid line.

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: High pressure Climaveneta FOCS FC 4822

    what is the your suction pressure if it is too high in starting time it is better you start your system ( compressor) with %50 and after suction pressure comes down then go to high load .
    in blast freezer I start system with % 50 and close liquid solenoid valve and when suction pressure comes down valve comes on and system goes to high loads with monitoring current in compressor if it goes higher then our setting our load comes down to protect our compressor.

  6. #6
    Join Date
    Nov 2008
    Location
    romania
    Age
    47
    Posts
    45
    Rep Power
    0

    Re: High pressure Climaveneta FOCS FC 4822

    It is a water cooled condensor or a air cooled condenser ? What is the water temperature when you start the compressor ? Only one circuit give HP alarm or both ? The fan are working ? If the valve is no`t opening the alarm should be LP alarm no`t HP . Give more data . My telefon number is 0758239960

  7. #7
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: High pressure Climaveneta FOCS FC 4822

    The model no. is for an air cooled chiller Im 100% sure of that. unfortunately Koskoloi who started the thread is not bringing forth information for us to help him out.