    Reasons for High Suction super heat and low Discharge superheat



    Hi friends, We are having Macuay Chiler PEH 100 using refrigerant 134a
    Please advise me the probable reasons for:-
    1) High Suction Super heat.
    2) Low Discharge Super heat.
    Thanks.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Reasons for High Suction super heat and low Discharge superheat

    At the same time?
    Poor performance of the comressor?

    Care to elaborate a bit more?
    Pressures/temperatures would be handy...



    P.S. One thread is plenty.

  3. #3
    Join Date
    Jul 2014
    Location
    India
    Posts
    5
    Rep Power
    0

    Re: Reasons for High Suction super heat and low Discharge superheat

    Thanks for responding Viking. . . .no no both the problems will rarely occur simultaneously. . .I am not having any problem with the chiller Unit. . . .I have asked the question for fetching some knowledge from you guys which will help me understand a little basics. . .I have started looking these chillers recently. ..

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Reasons for High Suction super heat and low Discharge superheat

    OK,

    1) Poorly adjusted/functioning TEV/EEV or high heat load (=very warm water)

    2) Poorly adjusted/functioning TEV/EEV, basically a low suction super heat giving too much liquid back to the compressor. OR, the discharge pressure is too low.

    The normal fault on the discharge super heat is the reversed, HIGH discharge superheat which normally means that either you got a lack of refrigerant (or at least a lack of refrigerant flowing through the evaporator) or a high head pressure (for example due to a dirty condenser)


  5. #5
    Join Date
    Jul 2001
    Location
    Good bay
    Posts
    50
    Rep Power
    24

    Re: Reasons for High Suction super heat and low Discharge superheat

    +1 to The Viking.
    But, In a McQuay Centrifugal the discharge superheat will mostly be low all the time as they use the liquid injection system to reduce sound level, liquid is picked up from the condenser and sprayed just behind the Impeller helping in sound reduction.
    Setrite

    A group of Donkey's Led by a Lion can defeat a group of Lion's led by a Donkey

  6. #6
    Join Date
    Jul 2014
    Location
    India
    Posts
    5
    Rep Power
    0

    Re: Reasons for High Suction super heat and low Discharge superheat

    Thanks Viking and Setrite. . .
    What I understand that. . .
    1) In case of High suction super heat. . .the refrigerant charge may be less or the expansion valve might be malfunctioning or the Chilled water load is more(Temp high or flow high) . . .
    2) In case of Low discharge superheat. ..the refrigerant charge may be excess or the expansion valve might be malfunctioning or condenser pressure is high due to low cooling water flow or dirty condenser tubes.
    Please let me know if I have understood correctly. .

  7. #7
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    48
    Posts
    186
    Rep Power
    20

    Re: Reasons for High Suction super heat and low Discharge superheat

    evrything else you said is correct except that if your water flow is low or condenser is fouled your discharge superheat goes up as well.

  8. #8
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Reasons for High Suction super heat and low Discharge superheat

    any thing can effect to evaporator capacity as same as you told about TX valve also evaporator fans - air flows from evaporator -
    Also in condenser air inside system effect to our condenser capacity and it is more common problem when we repair system.

  9. #9
    Join Date
    Jul 2014
    Location
    India
    Posts
    5
    Rep Power
    0

    Re: Reasons for High Suction super heat and low Discharge superheat

    Thanks PRESS and mbc. . . .

Posting Permissions