21-07-2014, 02:10 PM #1
Carrier 38/40GXQ with 49' line : factory charge is ok or extra refrigerant?
Hi there,
I bought a Carrier 38/40gxq. (With 1/4 & 1/2 refrigerant line)
When the company installed it they said that the factory charge was enough to supply up to 65' of line. (I've got 49' line lenght here)
But i checked on carrier website the installation manual for this unit
(http://dms.hvacpartners.com/docs/100...8-40gx-5si.pdf) and found that they say something else!
If you look page 9 they say that the factory charge is good for 25ft, after that lenght you have to add 0.1oz of refrigerant per extra foot of piping...
It make 2 days that the unit seem to work fine. I tested the heat mode and it seem to work well too...
So this is ok??
Thanks ahead of time for your response!
21-07-2014, 10:11 PM #2
Re: Carrier 38/40GXQ with 49' line : factory charge is ok or extra refrigerant?
its 24oz short
21-07-2014, 10:37 PM #3
So from what you think with 49' of line, extra refrigerant is needed as the installation manual say??