Thread: searle ks70 evaporator bearers
-
18-07-2014, 09:09 PM #1
searle ks70 evaporator bearers
Does anyone know what the amperage draw should be for the evaporators bearing in mind there is two wired in series ,they are 110volt wired in series with a 240volt supply.
Last edited by cadwaladr; 21-07-2014 at 03:30 AM.
-
20-07-2014, 11:28 AM #2
Re: searle ks70 evaporator bearers
Each fan the amps you find on the nameplate and if 2 in serie, 2 x Amps as found on nameplate
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
20-07-2014, 11:51 PM #3
Re: searle ks70 evaporator bearers
Sorry the post should have said evaporator heaters
-
21-07-2014, 06:04 AM #4
Re: searle ks70 evaporator bearers
Hi Cad.
Check out the attached.
Grizzly
-
22-07-2014, 12:20 AM #5
Re: searle ks70 evaporator bearers
Got it sorted today! Found out that the heaters should take approx 9 amps each and should be wired in parrell contrary to advice given to me by a colleague,all up and running defrosting fine thanks for the help guys,now the invoice can be sent!