    Buffer tank for a heat pump with panels



    Hi can any body help we just quoting a job of high temperature of 80 degrees for only rads the kW is 16 there not a lot of room on the job do we have to have a buffer tank ? We have 12 refrigeration metal panels and a heat pump



  2. #2
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23
    You need to go back to the manufacturer of the equipment to get this info.

    We quote 20l p/kW

  3. #3
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Buffer tank for a heat pump with panels

    You need a different system. 80C and a heat pump (refrig panels or not) don't mix well. Boiler time or drop the load temp, sorry.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Buffer tank for a heat pump with panels

    What are panels make and model? Heat pump make and model?

  5. #5
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Buffer tank for a heat pump with panels

    Most air to water heat pumps are only designed with a maximum leaving water of 55c possibly up to 60C.

  6. #6
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Buffer tank for a heat pump with panels

    Make is the energy panel from Spain

  7. #7
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Buffer tank for a heat pump with panels

    Nowhere in the literature does it say 80C is achievable. I wouldn't put my name on that system, and I do a LOT of solar. Be careful.

  8. #8
    Join Date
    Feb 2014
    Location
    UK
    Posts
    26
    Rep Power
    0

    Re: Buffer tank for a heat pump with panels

    You're talking about the "thermodynamic" panels which are basically a sun heating flat panel hex for a heat pump.

    12 panels is a large amount, so I presume that you are looking to use them for space heating also in which case you need a stratified thermal store, not a buffer tank, and yes you have to have one else you'll waste all the heat from the "thermodynamic" panels (the ones that freeze up on the surface in UK winters....)

    This is what you need : http://www.akvaterm.fi/eng/Accumulat...A_GEO.206.html you'll just about get away with the 300 litre version

    and no there is no way around it

    You don't need the solar version - that is for solar thermal systems.

  9. #9
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Buffer tank for a heat pump with panels

    We are using this system In Portugal for 3 months a year

  10. #10
    Join Date
    Sep 2014
    Location
    usa
    Age
    34
    Posts
    1
    Rep Power
    0

    Re: Buffer tank for a heat pump with panels

    Quote Originally Posted by MikeHolm View Post
    Nowhere in the literature does it say 80C is achievable. I wouldn't put my name on that system, and I do use solar energy. Be careful.
    Thanks for your advice.. Well I will be careful..I was going to make similar mistake but now I will be careful..
    Last edited by NewtonJuns; 23-09-2014 at 06:36 AM.