    Mains voltage



    What is the voltage range typically seen in Europe/UK 230V line?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Mains voltage

    I 've measured down to 225 and up to 258.
    Normally see 245 ish but officially it's 230. I only use 230 for designing circuits and calculating volt drop

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Mains voltage

    .

    I've measured from 218v upto 252v.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Mains voltage

    That's what I wanted to hear. I had a Viessmann boiler with issues that we couldn't explain and the early condensing boilers had 120V to 230V transformers in them so they could use the Euro product. We were measuring 247V and the Viessmann tech thought it might be too high. I didn't believe him and i was right. Bad trace connections on a board was the issue. sorted.

  5. #5
    Join Date
    Jan 2008
    Location
    England
    Posts
    25
    Rep Power
    0

    Re: Mains voltage

    Official guidelines 230v -5% +10% 217v...............253v