Results 1 to 5 of 5
  1. #1
    Join Date
    Mar 2012
    Location
    UK
    Age
    32
    Posts
    5
    Rep Power
    0

    Airedale Easicool downflow EEV control



    Hi guys,

    I'd like your thoughts,

    I was attending a breakdown the other day on an Airedale Easicool downflow system (out on HP, turns out it was a condenser fan motor seized which blew a fuse on the HPC). When I restarted the system the distributor iced up like nothing I've ever seen before!

    I had been to the system before with another engineer, removed the refrigerant (48kg of R407c), replaced all schrader cores (2 were leaking) and re-commissioned with 41kg (charged to the sight glass and had about 7k of superheat).

    So to me it doesn't seem like its short of charge (sight glass is full for a good few minuets), it looks like it could be the EEV.

    I went to another unit and checked the movement of the EEV on the controller which was fluctuating between 700 and 800.

    The unit in question was stuck on 480, even after we manually opened it to about 800.

    Is it worth re-removing all of the refrigerant and changing the EEV itself, or should I just change the EEV driver?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Airedale Easicool downflow EEV control

    I'd just change the EEV stepper motor first.

    I've had a few Carel ones fail, it's the cheaper option too.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2012
    Location
    UK
    Age
    32
    Posts
    5
    Rep Power
    0

    Re: Airedale Easicool downflow EEV control

    I've got half a mind to switch the driver controllers over first.

    If the EEV goes above 480 steps I know its the controller, if it doesn't its the EEV itself!

    Thanks for the advice!

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Airedale Easicool downflow EEV control

    matt, if theyre linked on the lan network then if u swap driver controller then you need to swap adresses on the back of the front flap- tiny bank of dipswitches- near the ribbon cable that attaches the led,s that flash .

  5. #5
    Join Date
    Oct 2007
    Location
    Northamptonshire
    Age
    60
    Posts
    25
    Rep Power
    0

    Re: Airedale Easicool downflow EEV control

    Might be EVD4 drivers.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •