    Pressure control faults in low ambients- help required



    Hey forum
    Just after some advice and knowledge regarding bulb thermostats and low pressure controls mounted outside in ambients below 0 degrees Celsius. I've had a few jobs of late cutting out when ambients are low but running fine by the time I get there. I heard a while ago this could happen but I'd like to know more about it and why.
    Thanks guys



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Pressure control faults in low ambients- help required

    hi cool me , lookes like you need a cool start pack = sedgy

  3. #3
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Pressure control faults in low ambients- help required

    Bulbs on cap tube t-stats and also most TXV's can be "fooled" by low ambients. The volatile fluid in the bulb/cap tube assembly gets colder than set point and the first drop of condensate develops not at the bulb end but in the cap tube or for TXV's at the diaphragm housing. For the t-stat it will remain satisfied in spite of the bulb being warmer than set point because the internal pressure is determined by the coldest point in the assembly. For a TXV using the same refrigerant for the thermal assembly as the refrig circuit, the TXV won't feed with the diaphragm housing colder than the bulb....That is why both thermostats and TXV's come with "cross ambient" or "ambient compensated" charges, largely for OEM devices or occasionally heat pumps.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •