    LG LMU360CE CH33 mystery



    LG (aka Load of Garbage) throws error code CH33 high head temp which usually means low on *****. Added some r410a till air temp dropped to mid 50s. Worked for 12 hours then threw CH33 again. Pressures look good. Drawing about 25 amps at the breaker box. Ideas?



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: LG LMU360CE CH33 mystery

    Clean Condenser?
    Non condensables in the system?
    Faulty Discharge temp sensor?


  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: LG LMU360CE CH33 mystery

    living on a prayer, unless u degas it and weigh in the correct charge

  4. #4
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: LG LMU360CE CH33 mystery

    Quote Originally Posted by install monkey View Post
    living on a prayer, unless u degas it and weigh in the correct charge
    Wise words. Reminds me of the chemisty GCSE question, what's the softest know metal to man?







    Yep, Bon Jovi.

    Anyway, 25A, is that a bit high? Service manual here: http://www.coastalwinair.com/lg%20manuals/LMU360CE.pdf 5.9-16.6A in specs.
    Probes can be problematic but you might want to check the basics first.

    Cheers,
    Andy.
    Last edited by Tayters; 13-07-2014 at 11:17 PM.
    Health and safety first..........unless I'm in a hurry.

  5. #5
    Join Date
    Aug 2014
    Location
    Australia
    Age
    36
    Posts
    68
    Rep Power
    10

    Re: LG LMU360CE CH33 mystery

    I had That fault once on an LG 9kw split a/c
    Turned out to be a $18 faulty Discharge pipe sensor