Results 1 to 3 of 3
  1. #1
    Join Date
    Mar 2012
    Location
    United Kingdom
    Age
    42
    Posts
    63
    Rep Power
    13

    Thumbs up Pego 200 expert connections of safety .....



    Hi there its my first touch witch install of freezer with controller pego 200 expert and I am not sure where to connect ranco high and low pressure switch for safety of compressor .... Please any advice thanks.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Pego 200 expert connections of safety .....

    if theres a contactor or relay for the compressor then switch the live feed to (A1) throught the pressure switch - ranco pressure switches are rated for 16 amp

  3. #3
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Pego 200 expert connections of safety .....

    Or connect the pressure switches through common and inp1 compressor protection input .Set parameter In1 to 0 and parameter pc to 1 which is normally closed