10-07-2014, 08:10 AM #1
P-Trap standards(?) for Refrigerant Piping
Hi All,
Just a quick one... is there (or was there ever) a kind of Rule-of-thumb in making a P-trap in a refrigerant pipeline?
I tried cross-referencing/checking on plumbing books and procedures but it didnt gave me an assured answer other than that it'll work as long as there is a proper "seal". However we are talking about ref piping here so there might be a more better explanation to have.
Thanks in advance.
-
10-07-2014, 12:24 PM #2
Re: P-Trap standards(?) for Refrigerant Piping
Hmm,
I always worked on "at least the diameter of the bender"...
However, somewhere in the back of my mind I seem to have "minimum of 3 pipe diameters"
-
10-07-2014, 09:06 PM #3
Re: P-Trap standards(?) for Refrigerant Piping
"P" trap to be as small as possible so as not to collect any more oil than necessary.
to my understanding it is not like a water "P" trap, but a trap where the oil droplets will collect & return in the gas flow down the suction line.
The oil is miscible with the refrigerant so mixes with the flow over it.
If your traps are to big they can collect to much oil out in the system.