    johnson controls on walk in freezer



    Client complaint ice on the floor in walking freezer, got to site Frozen droplets on ceiling and ice on floor defrost cycle obviously condensing and dripping onto floor, what I want to do is check the defrost intervals, temperature termination setpoint etc to identify problem but I cannot find how to access parameters no where anybody know
    It's a cr-nt150-1 module

    Cheers



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: johnson controls on walk in freezer


  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: johnson controls on walk in freezer

    oh lower your defrost termination temp and have a 1-2 min drain time/dripping time, also dont start your evap fan till the evap coil is about 5 deg

  4. #4
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: johnson controls on walk in freezer

    thanks for the reply, I already have this manual but it does not actually tell me how to actually access the parameters im at a dead end until I can do that

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: johnson controls on walk in freezer

    you tried holding the set button in for about 10 seconds?

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: johnson controls on walk in freezer

    hold enter to programming functions for 10 secs and hy will show up(hysteris)

  7. #7
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    242
    Rep Power
    21

    Re: johnson controls on walk in freezer

    throw it into the bin and put a dixel/carel or the like onto it.

    they are a mega pita to navigate and get into and even harder to explain to someone over the phone compared to others.
    "Old fridgies never die, they just run out of gas!"

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •