Thread: Acid Test
-
09-07-2014, 11:52 AM #1
Acid Test
Hi Guys,
Any Thoughts appreciated, just went to carry out an Acid Test on a York Chiller, took the sample from the oil fill valve at the bottom of the compressor (scroll) and got a blast of refrigerant/oil, into the test bottle which turned yellow indicating high Acid levels, question is is this test still reliable taken from refrigerant and not pure oil?
Thanks for any help.
-
09-07-2014, 01:51 PM #2
Re: Acid Test
The test reacts to acid, in a certain quantity.
Where this acid is doesn't matter.
-
09-07-2014, 10:46 PM #3
Re: Acid Test
usually yorks leak on the sumps, just collect it off the bolt heads, good job the f gas police dont troll on here
-
10-07-2014, 10:21 PM #4
Re: Acid Test
yes still reliable. next time use charging line with ball valve on end