    Pressure drop in an evaporator coil.



    Dear Technocrats,
    I have designed air source heat pump for water heating, the technical details of it are as follows-

    Refrigerant used = 134a
    Cooling capacity = 32.4 kW
    Heating capacity = 47.62 kW
    Evaporating temperature = 10 deg. centigrade
    Condensing temperature = 70 deg. centigrade
    Suction superheat = 8 K
    Subcooling = 5 K

    In this system I have used fin tube type evaporator, while testing the system it is observed that the expansion valve outlet pressure (i,e evaporator coil inlet pressure) is 80 psig which is much more than the designed pressure of 46 psig and evaporator coil outlet pressure (Suction pressure) is 30 psig which is less than designed pressure.

    So to check why it is happening I used a plated type heat exchanger instate of fin tube type evaporator coil then it is found that the expansion valve outlrt pressure and the suction pressure are as per the design i,e 46 psig.

    Kindly guide me why the pressure is getting dropped in fin tube type evaporator coil.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pressure drop in an evaporator coil.

    Tube resistance.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Pressure drop in an evaporator coil.

    as said above, thats why you need an externaly equalised valve when doing tube types.
    Now in Redvers Sask.

  4. #4
    Join Date
    Sep 2007
    Location
    New Delhi, India
    Age
    37
    Posts
    14
    Rep Power
    0

    Re: Pressure drop in an evaporator coil.

    You said its a heat pump? Water to Water system or Air to Water? since you have designed it for 10DegC Evapurating Temp, it needs be maintained across the Evp Heat exchanger to have steady Suction Pressure. Usually in Air to Water system, Variable Fan resolves this issue, for Water to Water you will need to have modulation valve to control Suction Pressures.