    what might be the issue if getting frost (icing) on narrow ***** pipe ?



    what might be the issue if getting frost (icing) on narrow ***** pipe ?

    what might be the issue if getting frost (icing) on broader ***** pipe ?

    What do we call the narrow pipe ?

    and what do we call the broader pipe ?

    thanks



  2. #2
    Join Date
    Jul 2014
    Location
    Pakistan
    Posts
    2
    Rep Power
    0

    Re: what might be the issue if getting frost (icing) on narrow ***** pipe ?

    17.jpg11.jpg12.jpg13.jpg14.jpg

    here are the images for your info

  3. #3
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: what might be the issue if getting frost (icing) on narrow ***** pipe ?

    Small pipe = liquid line (High pressure to medium pressure fluid)
    Big pipe = suction line (Low pressure gas)
    orifice = expansion device (Transision of high to low pressure)

    depending on make of system some frosting can be called normal mode of opperation, if there is lots of frost forming while system performs poorly, some gas may have leaked.

    from your images it looks like normal opperation, and the expansion device is inside the out side unit.

    I would recomend you repair the insulation on the narrow pipe with new insulation, as with any places needed ont he wide pipe.

    Is the inside coil making cool air?
    Is the wide pipe cool feeling as it leaves the coil?

    If no then you need a technicition to test the system and possibly add gas(you called it *****) to it
    Now in Redvers Sask.

  4. #4
    Join Date
    Aug 2005
    Location
    uk
    Age
    46
    Posts
    82
    Rep Power
    19

    Re: what might be the issue if getting frost (icing) on narrow ***** pipe ?

    Sog..........

  5. #5
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: what might be the issue if getting frost (icing) on narrow ***** pipe ?

    The small pipe on an ac unit is the expansion line, the expansion valve on most splits is inside the condenser, usually frosting of the expansion line is sog or EEV problem, that's if it is a split type system. Judging by the pictures both lines are insulated which indicates it is an expansion line not a liquid line

  6. #6
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    48
    Posts
    184
    Rep Power
    20

    Re: what might be the issue if getting frost (icing) on narrow ***** pipe ?

    You are evaporating your unit below 0degC. investigate:
    1. Low load on the evaporator which can be due to factors including fan not circulating enough air through the coil, blocked filters and clogged evaporator
    2. low refrigerant charge which may be due to leaks