    LG CH06 fault



    Hi all, I got called to a ducted LG split unit today thats out on a CH06 fault. I dont deal much with LG.
    I reset the controller and powered down the unit but it will not clear the code or attempt start all. Disconnected indoor pipe thermistor, measured 7.5k ohms at aprox 18 deg C. Voltage across sensor plug when connected is 2.7vdc. I have 5vdc from the board. Can anyone advise me of what the voltage out of the board with sensor disconnected should be. When i contacted LG tech support they could not tell me what that voltage should be only that my 2.7vdc with sensor connected is incorrect.
    Unit details; Indoor B30AHYN661 Outdoor B30AHYUE61
    Thanks.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: LG CH06 fault

    Indoor outlet pipe sensor
    • Open / Short
    • Soldered poorly
    • Internal circuit error
    Normal resistor : 5KΩ/ at 25°C (Unplugged)
    Normal voltage : 2.5Vdc / at 25°C (plugged)

  3. #3
    Join Date
    Mar 2014
    Location
    Australia
    Posts
    36
    Rep Power
    0

    Re: LG CH06 fault

    Thanks install monkey, looks like the sesnor is around the mark. I am just trying to make sure the voltage out of the board is correct or incorrect before deciding to change. If it is higher than supposed to be then voltage across the sensor will be incorrect.

  4. #4
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: LG CH06 fault

    Generally feed to pins on PCB would be 5V DC when probe unplugged.
    Health and safety first..........unless I'm in a hurry.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: LG CH06 fault

    stick a fixed resistor on it as a temporary to see if sensor is going out of range intermittantly or if it is failing when voltage is applied

  6. #6
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: LG CH06 fault

    http://www.lgcomfortcooling.co.uk/te...ype=faultcodes


    Mine of info here. If a residential unit then 06 an inverter current error although could be brought up from dodgy condenser probe if I recall. Think definition of residential is a wall mount, otherwise commercial.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  7. #7
    Join Date
    Mar 2014
    Location
    Australia
    Posts
    36
    Rep Power
    0

    Re: LG CH06 fault

    Thanks for the info everyone.