    Daikin FHYC140KVE8 - RY140LUY1



    Hi guys

    i have an E4 error code coming up on this unit.


    I have checked the LP switch on the outdoor unit and bridged it out but the error still occurs. The unit actually never runs as soon as the unit it turned on the error code appears straight away.

    I have checked the outdoor wiring diagram and there is a note on the LP sensor saying the following.





    I have checked the HAP light and it does flash when I take out the no 2 terminal wire.

    Has as anyone come across this before? It has really stumped me.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin FHYC140KVE8 - RY140LUY1

    E4 is a comms error between Indoor and outdoor pcb's.
    You have a K series indoor unit and an L series outdoor unit.
    These are not compatible

  3. #3
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Daikin FHYC140KVE8 - RY140LUY1

    The plot thickens then! I'm probably looking at the wrong condenser!

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin FHYC140KVE8 - RY140LUY1

    It must be Dementia onset...doh!

    E4 is Low Pressure Switch...U4 is Comms error

    In my defence, I've had a long few days and not much sleep....honest :-)

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin FHYC140KVE8 - RY140LUY1

    had it on a panasonic urban- all runs ok, alarms when not there, ended up replacing the comp contactor, all sorted

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin FHYC140KVE8 - RY140LUY1

    green hap led should light flash as soon as powered up to show comms

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin FHYC140KVE8 - RY140LUY1

    Is there any procedure for reseting alarms? It may be necessary to reset alarm after it's occurrence, and after it's cause has been eliminated.

  8. #8
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: Daikin FHYC140KVE8 - RY140LUY1

    All good.
    I had the wrong condenser. The coil has a leak on it and it has no gas. Hence the fault code.

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin FHYC140KVE8 - RY140LUY1

    OK, thanks for the update.