    Thermostatic expansion valve orifice size for variable loiads



    I would like to have ideas when selecting the orifice size for variable loads like ice cube makers or ice cream batch freezers. Where the refrigeration load is different at the beginning of the freezing cycle from the load at the end of the freezing cycle.

    When selecting the size of the orifice, should we consider the load at the beginning of the freezing cycle, the load at the end of the freezing cycle or the load at middle point?



  2. #2
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    48
    Posts
    186
    Rep Power
    20

    Re: Thermostatic expansion valve orifice size for variable loiads

    you size with your peak load which is the initial load value at the beginning of the cycle.

  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Thermostatic expansion valve orifice size for variable loiads

    when you design system you calculate all load then you choose in how many hours you want to cover it
    and then you choose your compressor - condenser and evaporator and...

    In cool rooms :
    your size comes from your evaporators capacity (actual evaporator capacity = evaporator loads-type of gas you choose- rooms temp -evaporator temp. and humidity )) when you choose size you should look for drop pressure in expansion valve --((discharge pressure - suction pressure))

    In this type of work it comes from evaporator capacity ( when you choose size you should look for drop pressure in expansion valve --((discharge pressure - suction pressure))
    Last edited by mbc; 25-07-2014 at 06:02 AM.

  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,645
    Rep Power
    23

    Re: Thermostatic expansion valve orifice size for variable loiads

    yup as said befor, you start with your heat load total / by time this gives the evap and TXV needed (But the final txv will be determined by plant)

    With total BTU/H we can size a plant, for this we need to know ambient, Compressor is sized for load, condenser is sized for ambient heat with some head room.

    For example: My place needs 1.5tons of cooling for air conditioning My txv will be from 2.02tr to 1.5tr through its operating range based on sub cooling.

    I have a 17000BTU/H rotary compressor and I am using a 2 ton condensing coil with a fan cycling switch.

    These combinations maximizes the efficiency and performance of each system.

    the natural function of a txv will reduce capacity as the load pulls down.
    Now in Redvers Sask.

  5. #5
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: Thermostatic expansion valve orifice size for variable loiads

    You Can choose the TXV and orifice @ design condition. Choose the one which loads 80%(TXV loading) at design condition , so that it gives enough capacity during pull down. As you know the valve capacity depending on the pressure drop across it. I generally select valve loading 80% and generally do not find any capacity issues with varying load