    carel pboohoo controller alarm



    Hi everyone hope you can help with this little problem.Controller keeps going into alarm which also turns off evaporator fan.with the alarm set at 5c and the cab temp at -6c it still goes off and shuts off the fan.any ideas folks. Thanks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: carel pboohoo controller alarm

    low temp alarm set at?

  3. #3
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: carel pboohoo controller alarm

    Low temp alarm set at -25c

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: carel pboohoo controller alarm

    intermittant faulty probe perhaps? going out of range but not enough to alarm on probe error

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: carel pboohoo controller alarm

    Hi. doormaster2008.
    Just a guess but if parameter A4 is set to 9.
    Then you may have an issue with the door switch?
    Worth checking anyways!
    Good Luck.
    Grizzly

  6. #6
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: carel pboohoo controller alarm

    Thanks guys.will checm them out.it seems strange if i switch mains off when in alarm condition when i switch it back on it will work for hours with no problems.

  7. #7
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: carel pboohoo controller alarm

    Seem to recall there are 2 types of alarm setpoints.

    Absolute where the temp (high and low) are the actual alarm threshold parameters.
    Relative where the alarm (high and low) are, well, relative to the setpoint.

    So if you are set for 1*C relative points of AL=5 then the alarm will come on at -4*C. If you have it set for -5 the it comes on at 6*C.
    A1=0 is relative
    A1=1 is absolute

    If AL or AH =0 then the alarm function is turned off.

    Not sure about the evap fans going off mind and if this is the alarm then you get AL or AH flashing up I think. When power is reset then you need to wait for the alarm delay before it alarms again.

    Carel, gotta love them. More settings than you can shake a stick at. Stick in an Elliwell. :-)
    Health and safety first..........unless I'm in a hurry.

  8. #8
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: carel pboohoo controller alarm

    Your not wrong there Taters.if the slot was'nt so long it would have an elliwell on it.dont know why they have to make everything so complicated.I cant understand why the fan stops.the alarm triangle and the cabinet temp readout flash on and off.I hate Carel.

  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: carel pboohoo controller alarm

    Hi doormaster2008.
    I agree Taters is more likely to have sussed your problem.
    Do you need a manual or have you one?
    Grizzly