r404a freezer walk in
have r404a freezer was very low on ref. charged it up clear glass, 240/30-35 box temp is low 20's ran for a while now icing back to compressor?
-
22-06-2014, 04:44 PM #2
Re: r404a freezer walk in
Whats the problem with it?
Mostly found in Oxfordshire, UK :)
-
22-06-2014, 05:17 PM #3
Re: r404a freezer walk in
Did you charge with liquid or vapour?
-
23-06-2014, 01:58 AM #4
Re: r404a freezer walk in
icing back to comp,thats not good right?
-
23-06-2014, 01:59 AM #5
Re: r404a freezer walk in
liquid,isnt icing a problem?
-
23-06-2014, 03:20 AM #6
Re: r404a freezer walk in
System lost part of refrigerant charge, 404a will fractionate. Recover system charge then evacuate and start again with new refrigerant, liquid charge after fixing the leak.
-
23-06-2014, 09:21 PM #7
Re: r404a freezer walk in
When you say it's icing back to comp do you mean onto the compressor body? R404a at that temp will frost suction line right back to to the comp service valve during normal operation but should not frost onto comp body. If you have frost on comp body this would suggest liquid yes and you should check your expansion device and superheat.
-
23-06-2014, 11:02 PM #8
Re: r404a freezer walk in
thanks for the advise will check out if they send me back to site