    Daikin



    Looking for input on a daikin wvrv.
    i am missing some units when addressing and one bs box
    unfortunately I can't get to bs box anymore.all the other units seem to address
    and I can run the fan on them till I finish the commissioning stage.one controller will not let me turn the fan on as it is centrally locked out.there is no ITM or backnet connected.
    any tips on best way to find the missing unit.there are also no spurs on the system but all power is on to indoors
    thanks



  2. #2
    Join Date
    Oct 2013
    Location
    England
    Age
    36
    Posts
    147
    Rep Power
    14

    Re: Daikin

    If you are 100% that you have power everywhere then the fault is most likely to be on your transmission wiring. Do you have multiple FCUs connected to 1 bs box? If so I'd say the missing FCUs and the missing box might well be connected. You say you can't get to the bs box anymore but I think you are going to have to as my guess is that the f1 f2 connection outdoor side has been forgotten/ pulled out or likewise with mains power into box. From what you have told us that is definitely where I would start. Failing that eliminate every other possible cause by checking all connections and power at every FCU/ box which is still accessible. Start at the beginning and make your way round, belling out every leg of cabling on the way to ensure it hasn't been chopped. Can be a long process...

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin

    look for green flashy led's on pcbs- shows communication

  4. #4
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    16

    Re: Daikin

    Found one bs box.still looking for the last fcu.very stressfully.
    can anyone tell me on the daikin service checker type 3 were does it tell me the water inlet/outlet temp on the display screen.

  5. #5
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    16

    Re: Daikin

    When I have found the last unit would I be better off doing a master reset.turning off outdoors and holding reset for 30 seconds when they are switched back on.
    cheers

  6. #6
    Join Date
    Oct 2013
    Location
    England
    Age
    36
    Posts
    147
    Rep Power
    14

    Re: Daikin

    Quote Originally Posted by ballvalve View Post
    When I have found the last unit would I be better off doing a master reset.turning off outdoors and holding reset for 30 seconds when they are switched back on.
    cheers
    Yes definitely master reset. Think 15 seconds of holding button in is sufficient. Just saved 15 seconds of your Saturday!

  7. #7
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    16

    Re: Daikin

    Cheers Newman ref
    any input on checker screen for water inlet/outlet temps.

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin

    then after the master reset youll have to do the wiring check- good for a saturday overtime and then the auto charge if vrv3,4
    Quote Originally Posted by NewmanRef View Post
    Yes definitely master reset. Think 15 seconds of holding button in is sufficient. Just saved 15 seconds of your Saturday!

  9. #9
    Join Date
    Oct 2013
    Location
    England
    Age
    36
    Posts
    147
    Rep Power
    14

    Re: Daikin

    Unfortunately I can't help with the service checker but I would say a good old touch probe could tell you just as accurately!

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin

    cant post service checker manual yet- keep getting this
    Forbidden

    You don't have permission to access /forums/newreply.php on this server.

    Apache Server at www.refrigeration-engineer.com Port 80

  11. #11
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin

    r it should be on the operation data display page.

  12. #12
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin

    Quote Originally Posted by install monkey View Post
    cant post service checker manual yet- keep getting this
    Forbidden

    You don't have permission to access /forums/newreply.php on this server.

    Apache Server at www.refrigeration-engineer.com Port 80

    me too.........