Results 1 to 2 of 2
  1. #1
    Join Date
    Jun 2014
    Location
    Portugal
    Posts
    1
    Rep Power
    0

    Exclamation AUX ASW-H12A4/SAR1DI fault - Error E5



    Hi all,

    My costumer has a AUX ASW-H12A4/SAR1DI with E5 error message. When I turn the AC on, the indoor unit starts "normally" and after around 5 minutes it shows the error message E5.

    The outdoor unit never starts at all. I've tested the AC for cool and for heat. Same happen.

    I found the service manual and E5 error is "fault of the indoor EEPROM".

    Should I have to change the indoor unit board, or simply reprogram the EEPROM? I could try to reprogram the EEPROM, but where can I find the file?

    I leave you the service manual link, if you want.


    Thank you in advance and best regards from Portugal!



  2. #2
    Join Date
    May 2010
    Location
    portugal
    Age
    44
    Posts
    29
    Rep Power
    0

    Re: AUX ASW-H12A4/SAR1DI fault - Error E5

    Boas! Reprogramares uma eprom? Nao, troca a placa