    Mhi vrf 407c e5 fault



    got an old 407c vrf Mitsubishi heavy industries system that is taking comp out for fun. latest fault is e5. found system with no gas . Found leak and repaired and re charged. but still unable to get comp to run. checked windings to earth and no resistance . Unable to give the model of comp but does any one know what resistance value i should have on a 3 phase inverter driven comp ? Could a faulty inverter take out comp, or would the loss of oil from the leak take the comp out before faulting on a low pressure fault?



  2. #2
    Join Date
    Nov 2008
    Location
    scunny!
    Age
    35
    Posts
    302
    Rep Power
    22

    Re: Mhi vrf 407c e5 fault

    Have you checked running amps ? Could be seized

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mhi vrf 407c e5 fault

    e5 transmission error- indoor to outdoor

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mhi vrf 407c e5 fault

    resistance should be equal between any 2 windings usualy around 1-3 ohms

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mhi vrf 407c e5 fault

    manual.pdf
    link works-page 217 check power supply and noise filters are prone for failing