    r407c



    can i charge r407c in previous r22 ac unit



  2. #2
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: r407c

    Hi ishtiaq ali,

    the oil may be a problem - as it was using R22, it probably has mineral oil in it.

    R407C will not work with the mineral oil - it has to have synthetic oil (POE).

    Check what oil is in the unit.
    Tony

  3. #3
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: r407c

    If it's mineral oil, you'll need to do a number of oil changes until the mineral oil content is acceptable (acceptable depends on the oil manufacturer).
    You'll lose about 5% capacity with the R407c.
    Yes, it's do-able, it was a common retrofit when I lIved in the UK.

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: r407c

    .

    It is do-able but also check any seals inside the system.
    If there are any valves or fittings that have a seal on it,
    be aware that the seal might not stand up to the new
    refrigerant and oil mixture.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..