    Can I leave a system in a vacuum overnite?



    In my shop it has been a common practice to leave new self contained units in a vacuum overnite if we have run out of time for the day or if we suspect a very small leak. We come in he next day check to make sure the vacuum held, (no leaks) then proceed to charge the system with the appropiate refrigerant and finish the project. I have now been told that if left in a vacuum overnite moisture will permeate through the pores of the manifold hoses and contaminate the system.

    Can I get some feed back on this issue?

    Thanks, Ken



  2. #2
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Can I leave a system in a vacuum overnite?

    If you turn the pump off and you maintain a vacuum below 500 microns overnight, you don't have any problems with the hoses. Now, if you are leaving the pump on... I would have to rethink my answer.

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Can I leave a system in a vacuum overnite?

    For example, you have a low side hose with a small amount of leakage, but the hose has no leakage on the high side. If you are pulling a vacuum with a pump that can maintain a vacuum while the one hose permeates or leaks, then you could well be drawing moisture in some small proportion throughout the system, if you are leaving the pump on.

    If you only have one connection, then the hoses won't be a problem, but you do have the consideration of an internal leak in the piping.

    I don't think that maintaining a vacuum with the pump on is a good practice. Use positive shutoff valves to isolate the pump and insure your vacuum.

  4. #4
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: Can I leave a system in a vacuum overnite?

    Ok, I can see I need to clarify and redirect the question as;

    If I have the system hooked up overnite with a micron gauge connnected but isolated from the pump, which is off, it is acceptable if the micron rise is within 500 microns.

  5. #5
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Can I leave a system in a vacuum overnite?

    it is acceptable if the micron rise is within 500 microns.
    If the vacuum remains below 500 microns, yes it is acceptable. Not if it rises 500 microns.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Can I leave a system in a vacuum overnite?

    Ken, One thing I might suggest is the use of copper tubing for pulling a vacuum. Not 1/4" tubing, but probably 3/8" or 1/2". The connections can be any size you want, but I would recommend the larger tubing to reduce the pressure drop.

    There are also two types of hoses for the manifold gauges. The regular ones which are normally color coded, red, blue, and yellow. Or, you can get heavy duty hoses that are solid black (at least mine are).

    I always suspected the regular hoses of being permeable, so I started to use the heavy duty charging hoses for everything, except for extended vacuums for dehydration of systems. Then I used copper tubing.

  7. #7
    rbartlett's Avatar
    rbartlett Guest

    Re: Can I leave a system in a vacuum overnite?

    I once lent my vac pump to a guy working Heathrow a.p
    He hooked it up on vac and went over to the other side for a quick look at another job. He the went on a 2 week holiday!!

    My poor vac pump was a moltern mess which he never had the courage to show me...

    Cheers

    Richard

  8. #8
    Join Date
    Apr 2006
    Location
    Guess
    Posts
    61
    Rep Power
    19

    Re: Can I leave a system in a vacuum overnite?

    A guy I worked alongside a number of years ago who always left a new plant on vacuum for a couple of days, ideally over a weekend.

    He reckoned back then that it was the way to go and, to be fair, he never got much trouble from his installation and, from what I hear, he still does this and it's working well for him.
    If it was easy everyone would do it.

  9. #9
    Join Date
    Mar 2006
    Location
    England
    Posts
    35
    Rep Power
    0

    Re: Can I leave a system in a vacuum overnite?

    Quote: have now been told that if left in a vacuum overnite moisture will permeate through the pores of the manifold hoses and contaminate the system.

    Does this realy happen???

    I'm struggling to understand how. my gauge lines are spec'd to withstand pressures up to 500 psi.....

    ...If they can hold that sort of pressure, i can't see a little vacuum causing any issues.

    IMHO, the person who told you this either a) made it up or b) has the worlds worst set of gauge lines.
    Last edited by weeksy; 16-04-2006 at 03:02 PM.

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Can I leave a system in a vacuum overnite?

    There is no problem in leaving the vacuum overnight and over a fortnight as well.

  11. #11
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Can I leave a system in a vacuum overnite?

    Hi

    depends on the system size. A domestic probably won't need this, but an industrial system will need a number of days, dependant on ambient, what moisture is in there and what vacumn you feel is required to be held when the pump is off. Ammonia will not need the same vacumn as a small domestic.

    Gauges are fine for small jobs, I have made up lines a bit like hydralic (with a plastic inner tube) for slightly larger systems, and a 1/2" hydralic hose for larger systems.

    Kind Regards Andy.

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Can I leave a system in a vacuum overnite?

    I have worked on several large R-22 systems. The vacuum pumps were left on for weeks to dry out the system.

    Multiple pumps and cold traps galore.

    Just make sure to check the oil levels regularly.

  13. #13
    austech's Avatar
    austech Guest

    Re: Can I leave a system in a vacuum overnite?

    I frequently leave systems on vac over night or for a few days, with the vac pump running. This is after I am confident that there are no leaks by performing pressurisation checks and using the electronic leak detector in the system as there is no sense in sucking in moisture and other contaminants. I usually leak check the hoses, connections and gauge manifold before leaving it on vac. This applies to large refrigeration systems and those that have been contaminated.

  14. #14
    Join Date
    May 2006
    Location
    Canberra
    Age
    74
    Posts
    7
    Rep Power
    0

    Re: Can I leave a system in a vacuum overnite?

    Quote Originally Posted by rbartlett
    I once lent my vac pump to a guy working Heathrow a.p
    He hooked it up on vac and went over to the other side for a quick look at another job. He the went on a 2 week holiday!!

    My poor vac pump was a moltern mess which he never had the courage to show me...

    Cheers

    Richard
    On an electron microscope the vacuum pump runs continusly and only shuts down for an oilchange twice a year and last many years. Your pump most likly was contaminated and this wrecked it.

  15. #15
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Can I leave a system in a vacuum overnite?

    No it probly ran out of oil, not all pump systems are the same on how they deal with oil, vacuum pumps that I've seen consume the oil as they go needing refilling every X houres of run time. A closed circuit oil system will obviously rarly need any oil toped up of which I'd assume your E-Micro scope is using such a system.

  16. #16
    Harris Daniel's Avatar
    Harris Daniel Guest

    Re: Can I leave a system in a vacuum overnite?

    are you sure that there is no leak at all. If you are not sure, then it is not a wise thing to leave the unit on vacuum overnight...as the air may enter the unit and moisture may come in contact with lubricating oil of compressor ...which is not advisable.
    if at all you want to verify leak...it is better to leave the unit pressurised with Nitrogen and note the standing pressure....any drop in pressure next day will indicate a leak in the system.
    Thanks
    Harris Daniel.
    Box 4311. Dubai. United Arab Emirates.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. What is System balance?
    By shogun7 in forum Technical Speculations
    Replies: 56
    Last Post: 19-01-2006, 09:47 AM
  5. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •