    display chiller not getting cold enough



    Hi, New here and couldn't find any ideas on this
    I have an igloo chiller display cabinet
    been working fine, but suddenly doesn't get cold enough
    The fan is working on the condenser radiator and it is clean and not blocked.
    Pipes into it hot, and out are cold
    pump appears to be working as hot and slight vibration felt
    but top condenser radiator part in chilled part, get frosted one end, but not cool other end
    is there a usual reason this may happen?
    I assume as the frost forms the coolant must be ok
    temperature is set to 2 degrees, i have checked, but cabinet wont go below 9 degrees now