    Question Transcritical CO2 Gas cooler/Compressor relationships



    Hello all,

    I've been wondering about the performance data given by :
    Bitzer transcritical compressor

    In the performance data, above the critical pressure 70bars, it uses T(gc for gas coolers) instead of T(condensing). How is one supposed to relate the gas cooler and compressor performances using the graphical* method?

    * Conventional ways use Tc (X axis) and Qo(Y axis). With the introduction of T(gc), should the corresponding values of Qo be plotted on the same graph? or should the graph enter a new "transcritical performance region?"

    Or can anyone here point me to a good gas cooler manufacturer which provide performance data?



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Transcritical CO2 Gas cooler/Compressor relationships

    .

    On the R744 Ph chart, you draw the graph in the transcritical position,
    that way the amount of heat rejected in the gas cooler can be calculated
    but it the cooler gas does not turn to liquid until you drop the pressure
    of the liquid.

    R744 works in transcritical when the condensing temp is about 32 degC and
    subcritical when the condensing temp is below 32 degC (if I remember correctly)

    Regards