    Dynamic air conditioning E 5 error .



    I have same error with 2 split sistems from Dynamic . Running fine half an hour and after that e5 error appears and the sistem stop . Starting again and running fine again . I did a check on the sensors but are fine . I don`t have any documentation on this split . I belive is maybe a problem with the indoor fan but i am not shure . Please if anyoane had the same problem tell me what should i check ? I must say i have different sistems same error ..12 k 18 kBtu .



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Dynamic air conditioning E 5 error .

    http://www.mediafire.com/view/m4oua3...ice_Manual.PDF
    see if this shinco manual is similar- a lot of chinese stuff gets rebadged
    E5 driver error- inverter circuit?

  3. #3
    Join Date
    Nov 2008
    Location
    romania
    Age
    47
    Posts
    45
    Rep Power
    0

    Re: Dynamic air conditioning E 5 error .

    No is an On-Off split sistem .

  4. #4
    Join Date
    May 2014
    Location
    Bulgaria
    Age
    32
    Posts
    34
    Rep Power
    0

    Re: Dynamic air conditioning E 5 error .

    If you provide photos of the units (better of the outdoors) I might be able to recognize the factory and give you a list of error codes.

    E5 in most of the units is lack of communication between the outdoor and the indoor. Most probably indoor PCB problem.

  5. #5
    Join Date
    Nov 2008
    Location
    romania
    Age
    47
    Posts
    45
    Rep Power
    0

    Re: Dynamic air conditioning E 5 error .

    2014-06-11 19.45.34.jpg It`s a simple on-off sistem no comunication between Indoor and outdoor .

  6. #6
    Join Date
    May 2014
    Location
    Bulgaria
    Age
    32
    Posts
    34
    Rep Power
    0

    Re: Dynamic air conditioning E 5 error .

    Correct, it is not exactly communication, it is a "dry contact" being sent from the IDU to ODU.

    If it doesn't work, then you might get the error.

    However this label is not familiar to me at all... Unfortunately I can't help you with this unit.

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Dynamic air conditioning E 5 error .

    if all the sensors are giving the same resistance - indoor and outdoor, then check if your getting a signal to the outdoor- any condensate pumps with external fault contact, or some have a limit switch on the louvre motor- if they dont open fully then the unit just wont do anything

  8. #8
    Join Date
    Nov 2008
    Location
    romania
    Age
    47
    Posts
    45
    Rep Power
    0

    Re: Dynamic air conditioning E 5 error .

    No pump contact no floating switch . I just removed the electronic board and put a universal control board at 40 euro .....everything is ok now . **** China .