    Junction between capilary and evap stopping up after a few minutes of runtime.



    I'm kinda new to freezers, and systems running at such low temps/pressures, so I need a little help here.

    I just bough a very nice (almost new) fridge/freezer that did not work. Found someone had worked on it previous and left the system open. I sealed the system, ran a vacuum for 30 mins, and charged it with R134a to 3 lbs low side and about 115 lbs high side at 70F ambient. The evap coils iced almost to the end, and everything looked just great for about 10 mins. Then the low side went to 20" vacuum, and the high side went to 170. I fiddled with it for a few hours and finally found that if I heat the junction between the capillary and the evap coils, it will hiss and start freezing immediately and the pressures go back to normal again for a few minutes.

    My first assumption was moisture was freezing at that point and blocking the flow, so I put the system on a vacuum for about 6 hours and recharged and have the same problem. Is moisture still a possibility even after such a long vacuum or am I looking at another problem? Help!



  2. #2
    Join Date
    Jul 2001
    Location
    Good bay
    Posts
    50
    Rep Power
    24

    Re: Junction between capilary and evap stopping up after a few minutes of runtime.

    Since the refrigerant circuit was exposed to ambient conditions for a long, you will need to pull a good vacuum of 500 microns, this could take more than 30 minutes. Your right that it is caused due to moisture in the system that freezes and blocks the capillary.
    Setrite

    A group of Donkey's Led by a Lion can defeat a group of Lion's led by a Donkey

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Junction between capilary and evap stopping up after a few minutes of runtime.

    Be a good to put fresh oil in the compressor too if possible.
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Junction between capilary and evap stopping up after a few minutes of runtime.

    .

    As all the other say.

    Replace the dryer for a new one,
    vac down to 500 microns (1/2 a torr) for a
    good few hours. The level of the vac is much
    more important than the length of time.
    Then replace the refrigerant for new.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  5. #5
    Join Date
    Jun 2014
    Location
    Linden TN
    Age
    40
    Posts
    2
    Rep Power
    0

    Re: Junction between capilary and evap stopping up after a few minutes of runtime.

    Thanks, I ran a vacuum for 6 hours, my unit is old, but supposed to do 300 microns. I'm going to order a drier tomorrow, and maybe even install an automotive accumulator/drier in the suction line just for kicks and to see how it effects the system. (they call me crazy around here!) Thanks for the help, I didn't want to be cutting in to the cap tube for no reason!

    I will be installing R290 after I get the system stabilized on 134a as I would like to try to lower power usage. I live in a solar powered home, and every little watt counts!

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Junction between capilary and evap stopping up after a few minutes of runtime.

    change the oil in your pump too, once it gets wet it won't pull a good vac, had systems i've had to change pump oil four times to get dry