    R22 carrier split system Need help troubleshooting



    I am a maintenance manager at an apartment complex. I am green to refrigeration. Just got my EPA cert this year. But I am learning and researching every day.

    I have a system that initially the compressor wouldn't start. Checked capacitor and found it was dead. Now the compressor will start. But the low side is pulling a vacuum. High side is about 130 PSIG Compressor is making a slapping sound. (scroll compressor)

    I suspect either TXV is shot or filter drier (very skinny copper spun filter dryer) is plugged or both. Can anyone weigh in on this.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: R22 carrier split system Need help troubleshooting

    Or no refrigerant?

    To start with check the sub cooling and super heat.
    If you give us those figures and the actual pressures/temperatures this system operates with our guesses as to what might be going on in your system will be closer to the mark.

    Also, you question the TXV and drier... Why? Is there ice on them? A huge temperature difference across them?


  3. #3
    Join Date
    Jun 2014
    Location
    united states
    Posts
    5
    Rep Power
    0

    Re: R22 carrier split system Need help troubleshooting

    The reason don't think its low on refrigerant is I added .955 lbs (Data plate says it holds 3.5 lbs) and low side still immediately went back into 20 inch's of vacuum.

    The reason I suspect txv and or drier is this is acting just like an identical unit in the building next door last year. (We farmed that out to local hvac contractor) When the contractor was working on that one. He found a lot of oil in evap coil,TXV was faulty. He installed new filter drier Charged unit and started it. Ran fine for for about 1 min. Then went back to acting up. He came back the next day he recovered refrigerant, Cut out filter drier , blew nitrogen threw low side with service valve closed. When he done that a bunch of oil came out of high side line. Then installed new drier charged and everything was fine. after that.

    Thank you for your response.

  4. #4
    Join Date
    Jun 2014
    Location
    united states
    Posts
    5
    Rep Power
    0

    Re: R22 carrier split system Need help troubleshooting

    Here is a shot of the data plate. And current filter drier Just because I am currious of the proper description of this style.

    0613142125.jpg0614141002.jpg

  5. #5
    Join Date
    Jun 2014
    Location
    united states
    Posts
    5
    Rep Power
    0

    Re: R22 carrier split system Need help troubleshooting

    I will attempt to get a superheat on monday. Gave the resident a window shaker for the weekend.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: R22 carrier split system Need help troubleshooting

    drier looks a bit small for the capacity of the unit

  7. #7
    Join Date
    Jun 2014
    Location
    united states
    Posts
    5
    Rep Power
    0

    Re: R22 carrier split system Need help troubleshooting

    Quote Originally Posted by install monkey View Post
    drier looks a bit small for the capacity of the unit
    I thought so also.. When they installed these units they took out blue canister driers and put these ones in .. They replaced about half the units because of a hail storm. and a generous insurance adjuster.. I'm sure the maintenance manager at that time told the contractor to use the cheapest parts possible to make himself look good..

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: R22 carrier split system Need help troubleshooting

    As IM said, that's not a suitable drier, that one is a joke.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: R22 carrier split system Need help troubleshooting

    that drier is meant for a fridge or deep freeze!

    TXV is the last thing you should be suspecting start with the basics. coils clean? air flow? then from there suction/discharge pressures saturated temps real temps coil deltas. then we can say it is low, but first and formost the drier must be replaced with a proper one (This is what cuased your coil to flood with oil, lack of mass flow of gass! due to restriction, txv was fine on old unit from other place!)