    Hi Guys,
    can anyone help me on this one.
    If i dont have a badged charge weight on a split system can i charge it by the temperature readings on my gauges?
    andy
    Nov 2008
    scunny!
    35
    302
    22
    Re: Charging by gauge temperature
    Ideally you should find out from the manufacturer or work off your air off temp on the evap
    May 2012
    59
    1,528
    36
    I have a Refrigerant charge calculator produced by DEFRA,
    it is only a guide, but if you want a copy PM me your email
    and I will forward you it.
    I can't vouch for it's accuracy because I have never used it
    in anger but it is a starting point.
    Rob
    Jan 2009
    Canary Islands
    74
    144
    If no info is available recover any remaining refrigerant.
    Charge by measuring superheat will also get you a good starting point, and ensure that no liquid returns to the compressor. At the same time, note the weight of refrigerant added and you can mark the unit accordingly.
    Graham
    en boca cerrada no entran moscas