    Chilled water expansion tank/pressure vessel/accumlator/bladder tank?



    Hi
    just been drafted in to finish a chilled water system that is half way through installation.....loads of issues however one at a time......

    The system is on a mixed use building - 170 bed hotel, ballroom, theater, art gallery lalalalala

    approximate volume 1000m3 chilled water - with approximate 400 fcu's and 22 AHU's....

    The expansion and feed tank, open tank is a floor below the highest point and is currently sized at 2 m3.

    The temp range - 5/6 - 14 + Degs C. I would therefore add another 5/10 degs as a diversity factor.

    QUESTION:
    Can i add a pressure vessel? Can i reduce the overall size of the pressure vessel instead of the 2 m3? Feed for the system can be automatic on a pressure switch?


    Any advice???



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Chilled water expansion tank/pressure vessel/accumlator/bladder tank?

    Hi Andrew.
    1000m3 of chilled water is a lot of water, the specific volume and density change of water will be significant dependent on temperature changes. I have always used 2% of system volume as a header tank size factor. In your case 20,000 litres/ 10 tonnes a lot of weight in one spot, I would be inclined to use multi pressure compensation tanks spread around all the buildings.
    Check www. engineeringtoolbox.com A lot of information re- header tank sizing.

  3. #3
    Join Date
    Oct 2008
    Location
    Vietnam
    Posts
    23
    Rep Power
    0

    Re: Chilled water expansion tank/pressure vessel/accumlator/bladder tank?

    ok...no problems for that..
    The point at which the location should be ? Should it be higher than the flow and return on the closed loop system? (As heating systems the expansion tanks are always higher). The connection from the tank can be connected to the system by the pump on the return...?

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Chilled water expansion tank/pressure vessel/accumlator/bladder tank?

    Hi Andrew.
    header tank at highest point of complex and connect to lower pressure return water. Add auto air bleeders bottles all around the whole system. Plus after multi flushing of water in system and cleaning strainers, add chemical treatment to chilled water for PH control. Monitor PH regularly.