Thread: CO2 Bulk tank

  1. #1
    Join Date
    Mar 2006
    Location
    Philippines
    Age
    53
    Posts
    124
    Rep Power
    19

    CO2 Bulk tank



    Hi all,
    Any body has Idea for the load calculation for the CO2 reefer unit? reefer unit should start @ 300 psi co2 press & stop @ 200 psi co2 press.

    Volume=75 tons

    Suction ?
    Discharge 45C
    Refrigerant R404a

    Thanks,
    eric
    Last edited by guapo; 30-03-2006 at 09:01 AM.



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: CO2 Bulk tank

    Hi Guapo

    In short no but I have worked on them and selected units in the past. Experience and trial and error are the norm. I have seen some very poor matches between the coil in the tank and the conensing unit. Best check out a few similar installation in your area. Insulation on the tank would be important, North or South facing would be important as well as the surface area of the tank (facing south).
    Usage of CO2 is also important, if the tank has a large volume of CO2 drawn off every day it may not even need cooling.

    From Memory a tank this size would have a 10hp unit on it.

    Hope this helps.

    Kind Regards. Andy

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: CO2 Bulk tank

    You first have to know the heat load onto the CO2 storage vessel. As Andy stated the sun exposure is one important aspect of this. Another is the actual temperature difference across the vessel & insulation.

    The sun exposure and the temperature difference comprise the total TD across the vessel. When the heat enters the CO2, the CO2 flashes off. This causes the rise in pressure. By condensing the vapor, the pressure is maintained in the vessel.

    The actual liquid level in the vessel is the surface area exposed to the heat. This is where the flash gas comes from. The heat that enters the vapor space is negligible.

    As Andy said, you can either match up the condensing unit capacity when compared to an equivalent vessel size, or, you need to know the vessel construction and insulation and liquid level.

    Essentially, the cooling load of the condensing unit is equal to the boiling rate of the CO2 in the vessel.

    The equivalent cut-in pressure of the condensing unit should be such that the CO2 pressure is well below the relief valve setting of the CO2 tank. Is your CO2 tank rated for a pressure higher than 300 psig?

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: CO2 Bulk tank

    Hi guapo,

    I maintain these units for years.
    Tomco ones,
    The suction is between 20 to 25 psi, depending on ambient temp.

    We stop the refrigeration unit at 260 psi.

    Chemi

  5. #5
    Join Date
    Mar 2006
    Location
    Philippines
    Age
    53
    Posts
    124
    Rep Power
    19

    Re: CO2 Bulk tank

    Thank you guys for the reply,

    The insulation of the co2 is polyeurethane(6" thik). The tank is oval shape and totaly exposed to sun light. The tank working pressure is 400 psig.

    regards
    Guapo

  6. #6
    Join Date
    Mar 2009
    Location
    India
    Age
    39
    Posts
    5
    Rep Power
    0

    Re: CO2 Bulk tank

    Hi guys.am new to this industry.and am being give na task of computing the required referigeration load for a Vertical Co2 polyeurethane(6" thik) insulated tank.The problem is when continoulsy running the chiller for 8-9 hrs, the pressure drop is negligeble..ie when the Chiller was switched on, the pressure was 21bar and after continously running for 9 hrs the pressure inside the tank was 20.5 bar..
    Should it be considered that the chiller used is inssufficient.
    It would be great if you could give me a few inputs..Following are the tank details:
    Tank capacity: 10000T
    6"thk polyeurethane insulated vertical tank.
    Ref: R404A

  7. #7
    Join Date
    Mar 2009
    Location
    India
    Age
    39
    Posts
    5
    Rep Power
    0

    Re: CO2 Bulk tank

    sorry a small correction..the capacity is 10T...regret the mistake

  8. #8
    Join Date
    Dec 2006
    Location
    Mansfield
    Age
    57
    Posts
    231
    Rep Power
    0

    Re: CO2 Bulk tank

    I think its probably sorted now, the thread is 3 years old



    PP

Similar Threads

  1. surge tank on racks
    By frozen ocean in forum Supermarket Refrigeration
    Replies: 14
    Last Post: 25-08-2009, 03:22 PM
  2. evaporator tank milk
    By milton in forum Trouble Shooting
    Replies: 2
    Last Post: 22-06-2006, 09:18 PM
  3. size of glycol tank
    By guapo in forum Industrial
    Replies: 2
    Last Post: 16-03-2006, 04:57 PM
  4. oil in tank heat load calculation
    By abbasi in forum Fundamentals
    Replies: 7
    Last Post: 13-06-2005, 08:36 AM
  5. chilled water storage tank!
    By dchatta in forum Technical Discussions
    Replies: 4
    Last Post: 24-05-2004, 04:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •