    Post Remote condenser + heat recovery



    Two Bitzer screw compressor on R22 conected with heat recovery and then to air heat exchanger (Condenser).
    I calculate thet i need pipe NO 50 from two comressors and heat recover.Calculate for 250kW each circle,Tcond=55 C,Tevap=0C,liquid subcoling = 10C,superheat at suction=12C

    2 oil traps

    20m horizontal

    5m vertical distance

    4 elbow

    In this case I woul have 11m/s in discharge line and 0,8m/s in liquid line.So I thinking about reduction in discharge line to get 17m/s.

    This is all for full load but what when compressor start to unload I dont know steps.(25%,50% or 75% etc.)

    So you see I am afraid that due the unload I would hawe problem with velocity (oil return) to compressor.
    Althaugh Bitzer screw have oil separator inside.



    What is your sudgestion??



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Remote condenser + heat recovery

    You can't have a full canister and a drunken wife at the same time.

  3. #3
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Post Re: Remote condenser + heat recovery

    Yes but I dont wont to have past out wife.

    Renato

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Remote condenser + heat recovery

    Set the microprocessor to a very short maximum time for unloading, in order to make sure it won't work for long at reduced capacity. This will negatively affect temperature stability, but will positively affect reliability.
    Please note that 25% on bitzers is normally only used for starting and not for thermoregulation, otherwise you will most probably end up with a liquid injection request.

  5. #5
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Post Re: Remote condenser + heat recovery

    I have liquid injection on compressor.

    Renato

  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Remote condenser + heat recovery

    Quote Originally Posted by Renato RR
    Two Bitzer screw compressor on R22 conected with heat recovery and then to air heat exchanger (Condenser).
    I calculate thet i need pipe NO 50 from two comressors and heat recover.Calculate for 250kW each circle,Tcond=55 C,Tevap=0C,liquid subcoling = 10C,superheat at suction=12C

    2 oil traps

    20m horizontal

    5m vertical distance

    4 elbow

    In this case I woul have 11m/s in discharge line and 0,8m/s in liquid line.So I thinking about reduction in discharge line to get 17m/s.

    This is all for full load but what when compressor start to unload I dont know steps.(25%,50% or 75% etc.)

    So you see I am afraid that due the unload I would hawe problem with velocity (oil return) to compressor.
    Althaugh Bitzer screw have oil separator inside.



    What is your sudgestion??
    You velocity seems alittle low What sort of loss have you in K and what about your suction line, would that not be the critical one for oil return. 25% capacity on a bitzer, never heard of that, the ones I use are 50% minimum. I never use the capacity reduction except for unloaded start, all they are is just a hot gas by-pass port, not a slide unloader, the compressorjust overheats when unloaded.

    Kind Regards. Andy

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Remote condenser + heat recovery

    Yes, bitzers have 4 steps, that is 100% plus 2 unloaders (75 and 50) plus the 25 which should only be used for starting.
    I actually use just the 75%, no solenoid on the 50% and one solenoid for the intermittent oil injection.

  8. #8
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Remote condenser + heat recovery

    Quote Originally Posted by Renato RR
    Two Bitzer screw compressor on R22 conected with heat recovery and then to air heat exchanger (Condenser).
    I calculate thet i need pipe NO 50 from two comressors and heat recover.Calculate for 250kW each circle,Tcond=55 C,Tevap=0C,liquid subcoling = 10C,superheat at suction=12C

    2 oil traps

    20m horizontal

    5m vertical distance

    4 elbow

    In this case I woul have 11m/s in discharge line and 0,8m/s in liquid line.So I thinking about reduction in discharge line to get 17m/s.

    This is all for full load but what when compressor start to unload I dont know steps.(25%,50% or 75% etc.)

    So you see I am afraid that due the unload I would hawe problem with velocity (oil return) to compressor.
    Althaugh Bitzer screw have oil separator inside.



    What is your sudgestion??
    Discharge line 17m/s should be no problem. But how about suction line? 25% is only for start up(most suppliers will tell it. I think may you need to install liquid injection and keep watch oil level indicator in start operation and confirm oil system is OK

    rgds
    LC
    I hear...I forget;I see...I remember;I do...I understand

  9. #9
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Post Re: Remote condenser + heat recovery

    Yes you are right about 25%.This compressor have oil separator inside housing so that will give me some time until unload stops.

    Anywone have idea how much will oil separator slow the reduction of oil on suction line.
    Some sors claims 4-5 working hours.

    Should I instold ICS Danfoss pilot ventil to make bypass in case that heat recovery takes all heat from sistem?

    Renato

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Remote condenser + heat recovery

    bitzer has a very good demister on discharge, so I wouldn't worry, unless refrigerant owns a low isoentropic exponent (low discharge temperature, like 404).
    Try to keep the oil as warm as possible, and connect the oil switch level sensor, just to be sure.

Similar Threads

  1. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  2. Heat recovery and aquifer heat/cold storage
    By RicHoe in forum Supermarket Refrigeration
    Replies: 23
    Last Post: 23-06-2006, 01:24 AM
  3. heat recovery systems
    By Brutalic in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 19-05-2006, 01:01 AM
  4. Heat Recovery for Air Conditioning
    By Student Eng in forum Air Conditioning
    Replies: 5
    Last Post: 13-05-2006, 05:28 PM
  5. Remote condenser
    By Rfcont in forum Technical Discussions
    Replies: 7
    Last Post: 06-12-2005, 12:44 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •