Results 1 to 16 of 16
  1. #1
    Join Date
    Feb 2011
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Compressor totally iced down.



    Hi, can somebody please give me a hint on this issue? Totally iced down compressor. Refrigerant not totally evaporated before suction maybe? I haven`t take any measurements yet. Just turned of compressor when discovered. Thanks.
    Attached Images Attached Images



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Compressor totally iced down.

    Low load in the evaporator (frozen up, dirty, fans broke, etc), thermostat set wrong or broken (system running below design conditions), Faulty or incorrectly adjusted expansion device, other system component failure.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Nov 2008
    Location
    romania
    Age
    47
    Posts
    45
    Rep Power
    0

    Re: Compressor totally iced down.

    Maybe the contactor is welded , low air flow , and all what Monkey said .

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor totally iced down.

    Evaporating temperature?

    Ambient temperature?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Compressor totally iced down.

    Well to start with check the super heat...

    For whatever reason you got too much liquid coming back to the compressor.
    Any of the reasons mentioned above could contribute to this but assuming you have some sort of EEV or TEV controlling the flow of refrigerant it should automatically reduce the flow back to the compressor (to a certain degree, if there is no heat going in to the evaporator at all then it doesn't matter if the TEV reduces the refrigerant flow to a minimum)

    Is the TEV/EEV's temp probe properly attached to the suction line?
    Is there any bypass from the Liquid side to the suction?
    Is it multi stage on a single circuit? (if so the controls might be XXX)

    All these questions...


  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Compressor totally iced down.

    It seems the main suction line isn't iced...strange.

    Turn on the other compressor and stop the iced one and see if the same happens with the other compressor.
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Compressor totally iced down.

    If a low temperature application possibly the liquid injection has gone ballistic and flooded the can.

  8. #8
    Join Date
    Jun 2014
    Location
    Finland
    Age
    44
    Posts
    3
    Rep Power
    0

    Re: Compressor totally iced down.

    Quote Originally Posted by Karlsen View Post
    Hi, can somebody please give me a hint on this issue? Totally iced down compressor. Refrigerant not totally evaporated before suction maybe? I haven`t take any measurements yet. Just turned of compressor when discovered. Thanks.

    Take a look to shut off valve in suction line for this particular compressor, there is your answer.

  9. #9
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Compressor totally iced down.

    Quote Originally Posted by Juniku View Post
    Take a look to shut off valve in suction line for this particular compressor, there is your answer.
    Yes, the valve maybe is almost shuted off so an high pressure drop will occur and lowering the evaporating temperature. Even so liquid carried on the suction line is happening otherwise this wouldn't be occuring.
    To make progress is never good enough, I want to do better and better and better

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor totally iced down.

    @ Karlsen
    By the date on that image, you are probably have sorted that out, or you set up your date on camera wrongly!
    Last edited by nike123; 06-07-2014 at 10:53 AM.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor totally iced down.

    Quote Originally Posted by mellcon View Post
    Hiii
    Compressor gas is over charged please bleed the gas till the frost disappears.
    Where to bleed? In atmosphere, maybe!

    By what measurement or data or picture, presented from OP you can conclude that compressor is overcharged?

    I can safely assume only that compressor lower casing (low pressure part) is at temperature below freezing point of water for some time.
    That doesn't necessary mean that is anything wrong with it.

    I see now, you are here for advertising purpose.
    Last edited by frank; 06-07-2014 at 09:58 PM.

  12. #12
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Compressor totally iced down.

    what are the 90 degree brass units and their job?

    check the packles valve as well

    but just could be a very humid day, I have had systems in perfect health get a whole lot of frost on them, but the fact that makes me wonder about the valve as onlt after the valve do we see frost.

    perhaps debrie has restricted valve?

    to know check super heat befor the valve, then check after the valve move forward from there!
    Now in Redvers Sask.

  13. #13
    Join Date
    Jun 2014
    Location
    india
    Age
    35
    Posts
    4
    Rep Power
    0

    Re: Compressor totally iced down.

    i am working on carrier elite line . i am facing the same problem from last two days my set point temp in minus 18 but the temp is freez on 9.3 from last 6 hours please help me ASAP.
    thanks

  14. #14
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Compressor totally iced down.

    hi ,
    if you could tell us the gas your using , the suction and discharge temps , and the temperature? c or f = sedgy

  15. #15
    Join Date
    Jun 2014
    Location
    india
    Age
    35
    Posts
    4
    Rep Power
    0

    Re: Compressor totally iced down.

    i am using r134a , the container temp is 9'c.

  16. #16
    Join Date
    Jun 2014
    Location
    india
    Age
    35
    Posts
    4
    Rep Power
    0

    Re: Compressor totally iced down.

    sorry its minus 9'c