Results 1 to 16 of 16
    Feb 2011
    Norway
    10
    Compressor totally iced down.
    Hi, can somebody please give me a hint on this issue? Totally iced down compressor. Refrigerant not totally evaporated before suction maybe? I haven`t take any measurements yet. Just turned of compressor when discovered. Thanks.
    3,856
    Re: Compressor totally iced down.
    Low load in the evaporator (frozen up, dirty, fans broke, etc), thermostat set wrong or broken (system running below design conditions), Faulty or incorrectly adjusted expansion device, other system component failure.
    Nov 2008
    romania
    47
    45
    Maybe the contactor is welded , low air flow , and all what Monkey said .
    11,025
    Evaporating temperature?
    Ambient temperature?
    Feb 2007
    2,473
    45
    Well to start with check the super heat...
    For whatever reason you got too much liquid coming back to the compressor.
    Any of the reasons mentioned above could contribute to this but assuming you have some sort of EEV or TEV controlling the flow of refrigerant it should automatically reduce the flow back to the compressor (to a certain degree, if there is no heat going in to the evaporator at all then it doesn't matter if the TEV reduces the refrigerant flow to a minimum)
    Is the TEV/EEV's temp probe properly attached to the suction line?
    Is there any bypass from the Liquid side to the suction?
    Is it multi stage on a single circuit? (if so the controls might be XXX)
    All these questions...
    Dec 2008
    Portugal
    48
    1,020
    It seems the main suction line isn't iced...strange.
    Turn on the other compressor and stop the iced one and see if the same happens with the other compressor.
    Auckland
    74
    3,357
    37
    If a low temperature application possibly the liquid injection has gone ballistic and flooded the can.
    Jun 2014
    Finland
    44
    3
    Quote Originally Posted by Karlsen View Post
    Take a look to shut off valve in suction line for this particular compressor, there is your answer.
    Dec 2008
    Portugal
    48
    1,020
    Quote Originally Posted by Juniku View Post
    Yes, the valve maybe is almost shuted off so an high pressure drop will occur and lowering the evaporating temperature. Even so liquid carried on the suction line is happening otherwise this wouldn't be occuring.
    Split Croatia
    57
    6,151
    36
    @ Karlsen
    By the date on that image, you are probably have sorted that out, or you set up your date on camera wrongly!
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by mellcon View Post
    Hiii
    Compressor gas is over charged please bleed the gas till the frost disappears.
    Where to bleed? In atmosphere, maybe!
    By what measurement or data or picture, presented from OP you can conclude that compressor is overcharged?
    I can safely assume only that compressor lower casing (low pressure part) is at temperature below freezing point of water for some time.
    That doesn't necessary mean that is anything wrong with it.
    I see now, you are here for advertising purpose.
    Apr 2006
    41
    1,620
    what are the 90 degree brass units and their job?
    check the packles valve as well
    but just could be a very humid day, I have had systems in perfect health get a whole lot of frost on them, but the fact that makes me wonder about the valve as onlt after the valve do we see frost.
    perhaps debrie has restricted valve?
    to know check super heat befor the valve, then check after the valve move forward from there!
    Now in Redvers Sask.
    Jun 2014
    india
    35
    4
    i am working on carrier elite line . i am facing the same problem from last two days my set point temp in minus 18 but the temp is freez on 9.3 from last 6 hours please help me ASAP.
    thanks
    Oct 2008
    mallorca, spain,
    75
    768
    hi ,
    if you could tell us the gas your using , the suction and discharge temps , and the temperature? c or f = sedgy
    Jun 2014
    india
    35
    4
    i am using r134a , the container temp is 9'c.
    Jun 2014
    india
    35
    4
    sorry its minus 9'c