    Trane RTAD 180 MANUALS



    Hello guys . I have a problem with above Trane chiller and i need some wiring documentation .
    I have a Phase loss alarm on second compressor and i don`t know who is generating the alarm .
    Best regards .



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Trane RTAD 180 MANUALS

    Quote Originally Posted by texanul View Post
    Hello guys . I have a problem with above Trane chiller and i need some wiring documentation .
    I have a Phase loss alarm on second compressor and i don`t know who is generating the alarm .
    Best regards .
    Check the resistance of current transformer (CT) for compressor. Probably the CT will be defective.

  3. #3
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Trane RTAD 180 MANUALS

    Is it a UCM/CLD controller, or a CH530?
    As Moideen says, test the CT. Also (obviously) check the phases are balanced, no more than 10% from the mean value.
    Be aware that controllers on some Trane chillers have insufficient inputs to assign each possible fault it's own port. As a result, some faults will be tagged as the primary fault for that input, but actually be a secondary fault.
    Is there no paperwork with the chiller? Or an O&M manual on site?

  4. #4
    Join Date
    Nov 2008
    Location
    romania
    Age
    47
    Posts
    45
    Rep Power
    0

    Re: Trane RTAD 180 MANUALS

    I did a check on the current transformer and they are ok . All 6 of them have 62-64 ohm . 20140603_100224.jpg20140603_100206.jpg

  5. #5
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14

    Re: Trane RTAD 180 MANUALS

    Hi,
    If the compressor is not starting check the high pressure pressostat especially if it is a double one.
    If the compressor starts and then trips, several causes exist such as:
    Severe voltage unbalance,
    Defective current transformers,
    Defective compressor module (Try to swift modules, if you know how),
    Defective contactors, etc.
    Regards,
    CV

  6. #6
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Trane RTAD 180 MANUALS

    Quote Originally Posted by CV_Geardrive View Post
    Hi,
    If the compressor is not starting check the high pressure pressostat especially if it is a double one.
    If the compressor starts and then trips, several causes exist such as:
    Severe voltage unbalance,
    Defective current transformers,
    Defective compressor module (Try to swift modules, if you know how),
    Defective contactors, etc.
    Regards,
    CV
    dear cv-gerad,

    i want to know more about "swift module" which you mentioned. is this already integrated on control panel or any external device.

  7. #7
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Trane RTAD 180 MANUALS

    I think he meant switch? As in, swap the two compressor control modules & see if you still have the same problem, or if the problem moves with the module.
    This is a simple way to prove if it's the modules that are at fault.

    It's a UCM/CLD controller. I'll have a look, maybe I still have a wiring diagram for them.

    With regard to the HP switch; Yes, a lot of Trane gear has dual HP switches which can really mess with you if you're not familiar. Used to be mounted behind the forward end panels & at a glance it looks like a normal HP/LP switch. Where it's tricky is that both switches are manual reset, but there's only one reset button on top. The second reset is a small brassy looking press stud in the upper middle of the front. Take off the front cover of the switch & you'll see it.

    Are there any faults showing on the display? If the system is in fault, the red LED at the top right of the display module should be flashing , iirc.
    Last edited by FreezerGeezer; 04-06-2014 at 10:38 AM.

  8. #8
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Trane RTAD 180 MANUALS

    check the boot confirmation signal to the compressor module.

    not confirm the startup module interprets this as loss phase.
    all faults are presented in the panel even the pressure switch

  9. #9
    Join Date
    Nov 2008
    Location
    romania
    Age
    47
    Posts
    45
    Rep Power
    0

    Re: Trane RTAD 180 MANUALS

    My problem just disapeared after 2 days . Stupid problem . Thanks guys . Both compressors runnig fine now .

  10. #10
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Trane RTAD 180 MANUALS

    Good to hear (I think?). I've found some wiring diagrams if you want them?