    Has anyone every tested or experienced the energy savings on a coldroom by running 2 setpoints, a daytime setpoint and a night time/low load setpoint. Just say 1-3 degrees C during day and 3-5C at night.
    Has anyone tried it and measured power savings?
    Do you think it would add any power savings??
    Would the compressor running time really end up much less?, even though at night its not lowering it as much, would the running time from cycling it between 1-3, and 3-5 would make much of a difference.....????

    Anyones thoughts or experiences would be much appreciated...... thankyou



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: saving energy on coldroom

    air curtain, led lights on a pir , trimming the defrost duration would reduce costs- also inverter drive or soft start kit on the compressor, dc fans would help too

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: saving energy on coldroom

    Queensland?
    Haven't you got different electricity tariffs day/night?
    If so, which is the cheaper one?

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: saving energy on coldroom

    Cool room need to know if temp swing effects product, like milk.
    power is cheaper at night so you need to understand your power bill & tariff.
    Usually run colder at night tariff as power is cheaper.
    let temp float up during the day.

    That what big cold stores do if they can, but in freezer example with ice cream they like temp stable so not to affect quality.
    On larger jobs VSD on evap & compressor, run temp low as you can at night.

  5. #5
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    601
    Rep Power
    28

    Re: saving energy on coldroom

    Maybe it's worth considering an ice bank? Build it on cheap power & use it to reduce the cooling load in the day time.

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: saving energy on coldroom

    How big is this cool room, or is it just a general question?

  7. #7
    Join Date
    May 2010
    Location
    Queensland
    Posts
    36
    Rep Power
    0

    Re: saving energy on coldroom

    approximately 8 x 10m....... great point about the cheaper electricity at night guys

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: saving energy on coldroom

    Try to condens as much as possible and to evaporate as high as possible. This will give you the biggest savings.
    ECM fans as someone suggested.
    The only saving duing night is the lower DT over the panels, so smaller losses but very marginal. This will be not noticable at all in the total energy bill.
    It will be just the opposite I think: compressor will have to run at more expensive rates during the day to cool down the load again in the coldroom.
    Is a higher setpoint allowed for the products
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Nov 2008
    Location
    scunny!
    Age
    35
    Posts
    302
    Rep Power
    22

    Re: saving energy on coldroom

    Don't use it

  10. #10
    Join Date
    Oct 2013
    Location
    England
    Age
    36
    Posts
    147
    Rep Power
    14

    Re: saving energy on coldroom

    Link out the meter for 4 hours a day.

  11. #11
    Join Date
    Jun 2014
    Location
    TOYNTON
    Age
    33
    Posts
    1
    Rep Power
    0

    Re: saving energy on coldroom

    Any energy efficiency initiative dealing with refrigeration
    should start by reviewing the heat gains on your system.
    If you understand the nature of these gains, you’ll be able
    to manage the amount of cooling that needs to be done
    and make energy savings. Heat gains include warm air
    entering the cabinet or cold room and heat produced by
    electrical equipment within the cooled space. This guide
    covers in detail two opportunities to reduce heat gains:
    reducing cold air changes using strip curtains, and using
    EC (electronically commutated) replacement motors
    for evaporator fans.

    I read your site.I like it very much.I hope it will be good of people.
    I have a small website.If you want please visit this website a ber.
    Last edited by frank; 18-06-2014 at 05:54 AM.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •