Results 1 to 11 of 11
    May 2010
    Queensland
    36
    saving energy on coldroom
    Has anyone every tested or experienced the energy savings on a coldroom by running 2 setpoints, a daytime setpoint and a night time/low load setpoint. Just say 1-3 degrees C during day and 3-5C at night.
    Has anyone tried it and measured power savings?
    Do you think it would add any power savings??
    Would the compressor running time really end up much less?, even though at night its not lowering it as much, would the running time from cycling it between 1-3, and 3-5 would make much of a difference.....????
    Anyones thoughts or experiences would be much appreciated...... thankyou
    Oct 2007
    manchester
    44
    5,707
    Re: saving energy on coldroom
    air curtain, led lights on a pir , trimming the defrost duration would reduce costs- also inverter drive or soft start kit on the compressor, dc fans would help too
    Feb 2007
    2,477
    Queensland?
    Haven't you got different electricity tariffs day/night?
    If so, which is the cheaper one?
    2,565
    28
    Cool room need to know if temp swing effects product, like milk.
    power is cheaper at night so you need to understand your power bill & tariff.
    Usually run colder at night tariff as power is cheaper.
    let temp float up during the day.
    That what big cold stores do if they can, but in freezer example with ice cream they like temp stable so not to affect quality.
    On larger jobs VSD on evap & compressor, run temp low as you can at night.
    Aug 2001
    Gold Coast, Australia
    601
    22
    Maybe it's worth considering an ice bank? Build it on cheap power & use it to reduce the cooling load in the day time.
    2,565
    28
    How big is this cool room, or is it just a general question?
    May 2010
    Queensland
    36
    approximately 8 x 10m....... great point about the cheaper electricity at night guys
    Oct 2003
    56
    5,519
    28
    Try to condens as much as possible and to evaporate as high as possible. This will give you the biggest savings.
    ECM fans as someone suggested.
    The only saving duing night is the lower DT over the panels, so smaller losses but very marginal. This will be not noticable at all in the total energy bill.
    It will be just the opposite I think: compressor will have to run at more expensive rates during the day to cool down the load again in the coldroom.
    Is a higher setpoint allowed for the products
    Nov 2008
    scunny!
    29
    302
    Don't use it
    Oct 2013
    30
    147
    8
    Link out the meter for 4 hours a day.
    Jun 2014
    TOYNTON
    28
    1
    Any energy efficiency initiative dealing with refrigeration
    should start by reviewing the heat gains on your system.
    If you understand the nature of these gains, you’ll be able
    to manage the amount of cooling that needs to be done
    and make energy savings. Heat gains include warm air
    entering the cabinet or cold room and heat produced by
    electrical equipment within the cooled space. This guide
    covers in detail two opportunities to reduce heat gains:
    reducing cold air changes using strip curtains, and using
    EC (electronically commutated) replacement motors
    for evaporator fans.
    I read your site.I like it very much.I hope it will be good of people.
    I have a small website.If you want please visit this website a ber.