    Daikin rp71



    Have got a fault e3 found gas leak which I fixed but fault keeps coming back. Have noticed compressor starts but fan dosent pressure builds up to about 420 psi then fan starts unit runs fine for a few hours cycling fine compressor is fixed speed so fan shud start same time as compressor. Fan seams good any ideas am thinking outdoor pcb anyone who has similar problems could you help us out cheers



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin rp71

    2 speed cond fan, they start on low speed when comp starts- quick fix is to directly feed the fn off the out going side of the contactor- but fuse it for the fan

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin rp71

    Had that many times.

    I normally fit two auto-reset HP switches to control the fans directly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin rp71

    http://www.mediafire.com/view/7bp42c...m219-54886.pdf
    service manual- read about condenser fan control at start up-

  5. #5
    Join Date
    Feb 2014
    Location
    Liverpool
    Age
    46
    Posts
    24
    Rep Power
    0

    Re: Daikin rp71

    Ok fair enough but why is the fan not starting straight away hp switch seams ok it's a single fan condensor just strange it won't start till it gets to about 400 psi thought this fan was 1 speed

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin rp71

    if 4 wires on the fan plug its 2 speed,run it in heating mode and the cond coil will lightly frost for about 4 mins then the fan will start- ive even tried replacing relays on the pcb as no 240v output

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin rp71

    Also try moving the ambient air sensor from it's clip and push it into the coil fins.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Feb 2014
    Location
    Liverpool
    Age
    46
    Posts
    24
    Rep Power
    0

    Re: Daikin rp71

    Thanks for your help install monkey have tried opening your link but won't let me could you email it to me please thanks sjrowan@hotmail.com thanks