    Feb 2011
    Australia
    38
    3
    Stall on a centrifugal fan
    I have a fan on a large AHU that is shuttering at approx 60% speed, has anyone ever experienced 'stall' on centrifugal fans? Both pulleys new, belts new and definantly aligned.
    Anyone input would be appreciated!
    3,355
    Re: Stall on a centrifugal fan
    Quote Originally Posted by bunda View Post
    So bunda,
    Do you mean it vibrating like it's out of balance?
    Can only suggest you check fan blades intact, clean & not damaged.
    Check drive shaft is running true, as well as fan wheel.
    All supports & structure of it secure.
    Could also require balancing.
    If you speed it up past 60% does it come good?
    Feb 2011
    Australia
    38
    3
    So running on a variable speed drive, up to 30hz fan runs perfect, between 32-35hz I have this issue then as it runs higher it corrects itself again.
    11,025
    Is it the fan, the motor or the inverter that is causing the problem?
    manchester
    5,639
    maybe slow down the ramp up time- check the inverter is prog correctly for the motor size,rpm,flc etc- run it in hand at 50htz to test it
    3,355
    http://www.pump-zone.com/topics/moto...-and-solutions
    Suggest skip the frequencies causing the issues.
    A large backward curve centrifugal will stall overload if discharge air is blocked or restricted.
    Dec 2011
    42
    131
    14
    Had an issue like this on a trane unit, new inverter sorted it