    copeland compressor



    Hey I have a Copeland discus compressor, when the compressor power is turned off and the discharge valve is fully closed the pressure drops in seconds to the same pressure as the suction. Wondering what you think it is. Valves or internal relief


    Thanks



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: copeland compressor

    I'm not sure how you can tell, presumably the symptoms are the same in either case, though sometimes bad valves can whistle as the pressures equalise.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: copeland compressor

    Hi jsw
    As Monkey Spanners says it would be hard to tell if it is the valves or the relief, best thing to do is pull the heads off and inspect the valves and at the same time check the relief. It could also be a damaged head gasket.
    Paul
    Born to fish, forced to work

  4. #4
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    20

    Re: copeland compressor

    Is it a discus digital compressor? Does it have unloaders. Perhaps the suction valves default to an unloaded position when the power is removed. If so, maybe what you are seeing is system equalization?

    Just a thought?

  5. #5
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: copeland compressor

    it might be happen due to two reasons.

    1.if the system is overcharged,during the pump down the relief valve will bypass the excess gas.
    2.leakage of valves or valve plate.

    if you check the compressor head temperature if it is above 140c as it is working, the particular head is bypassing.