25-05-2014, 04:42 PM #1
Samsung Maldives Wired Controller
Hi, I have purchased a Samsung MWR-WE10 wired controller but I am trying to wire it up to the Samsung Maldives indoor unit by the labelling of the wire terminals does not match. On the indoor unit there is 1(L), 2(N), F1 and F2 and on the wired controller it is labelled F3, F4, V1, V2. How can I connect the controller to the indoor unit? Thanks.
25-05-2014, 05:02 PM #2
Re: Samsung Maldives Wired Controller
http://dvmdownload.com/controls/indi...al_English.pdf
controller install guide- says connect to f3,f4 terminals- you probably need an interface for a hard wired controller
25-05-2014, 06:37 PM #3
what is the exact model of the maldives indoor, because there are a lot of indoors with this design and some of them (RAC gamma) are not compatible with WE10. The SAC gamma is compatible, model code AC***FBRDEH.
25-05-2014, 07:07 PM #4
27-05-2014, 12:49 PM #5
Hi, unfortunately this indoor is not compatible with the WE10 remocon.
A model, which is compatible is: MWR-WH00
To connect it you will need, as install monkey suggested, an interface module, which gives you the communication (F3/F4) and the power supply (V1/V2). This subpcb is called MIM-A00