    Compressor Burn Out Help



    I have a 3~ Tecumseh compressor R404a.

    HP 12 Bar, a bit low
    LP 6 bar, a bit high

    Compressor appears to be pumping and sounds OK.

    However, oil and refrigerant stink like a burn out. Expansion valve filter is stained black but not blocked, maybe partially blocked but you can still see light through it.

    Filter drier removed and can be blown through !

    However there's very little cooling coming back from the evaporator, which appears to be starved, SH not measured but obviously very high.

    Refrigerant has been weighed, no signs of leaks, charge OK, has a receiver.

    Its an ice cream display counter, set point -14c.

    I have removed compressor and drained some of the oil, it's clear, smells acidic though.

    I'm fairly sure the compressor has had it but the pressures are confusing the hell out of me, any ideas whats going on anyone?

    Haven't checked gauges for a while...

    Thanks



  2. #2
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Compressor Burn Out Help

    Unless the 6 bar lp is a misprint i would be pretty sure your compressor valves are goosed

  3. #3
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Compressor Burn Out Help

    Your refrigerant is dead. It has broken down over time for one reason or another.
    Running a compressor with a high discharge temperature is one way.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Compressor Burn Out Help

    R404A 600kpa= 4.4degC so maybe system was off for a day or two when pressures were measured, or something crazy like that.
    Maybe use it for milk instead of ice cream

  5. #5
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Compressor Burn Out Help

    Quote Originally Posted by RANGER1 View Post
    R404A 600kpa= 4.4degC so maybe system was off for a day or two when pressures were measured, or something crazy like that.
    Maybe use it for milk instead of ice cream
    Ranger !,I'll stick with my opinion.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.