    Scotland
    312
    12
    Compressor Burn Out Help
    I have a 3~ Tecumseh compressor R404a.
    HP 12 Bar, a bit low
    LP 6 bar, a bit high
    Compressor appears to be pumping and sounds OK.
    However, oil and refrigerant stink like a burn out. Expansion valve filter is stained black but not blocked, maybe partially blocked but you can still see light through it.
    Filter drier removed and can be blown through !
    However there's very little cooling coming back from the evaporator, which appears to be starved, SH not measured but obviously very high.
    Refrigerant has been weighed, no signs of leaks, charge OK, has a receiver.
    Its an ice cream display counter, set point -14c.
    I have removed compressor and drained some of the oil, it's clear, smells acidic though.
    I'm fairly sure the compressor has had it but the pressures are confusing the hell out of me, any ideas whats going on anyone?
    Haven't checked gauges for a while...
    ireland
    48
    269
    Re: Compressor Burn Out Help
    Unless the 6 bar lp is a misprint i would be pretty sure your compressor valves are goosed
    Jul 2010
    NTH.QLD Australia
    56
    1,757
    26
    Your refrigerant is dead. It has broken down over time for one reason or another.
    Running a compressor with a high discharge temperature is one way.
    2,565
    28
    R404A 600kpa= 4.4degC so maybe system was off for a day or two when pressures were measured, or something crazy like that.
    Maybe use it for milk instead of ice cream
    Jul 2010
    NTH.QLD Australia
    56
    1,757
    26
    Ranger !,I'll stick with my opinion.