    C.o.p question



    If a system has a COP of 4 and an output of 9kw when in heating, would the cooling capacity be

    2.25kw or 6.75kw

    Thanks Chris



  2. #2
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: C.o.p question

    what do you understand by COP?

  3. #3
    Join Date
    Jun 2008
    Location
    england
    Posts
    15
    Rep Power
    0

    Re: C.o.p question

    RE/WD
    It's an exam question.

  4. #4
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: C.o.p question

    which I guess means you don't know.

    http://en.wikipedia.org/wiki/Coefficient_of_performance

    the equation is right there which will get the answer you need.

  5. #5
    Join Date
    Jun 2008
    Location
    england
    Posts
    15
    Rep Power
    0

    Re: C.o.p question

    I'm still confused by this...
    Last edited by combi99; 25-05-2014 at 11:38 AM.

  6. #6
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: C.o.p question

    Sorry I don't like just telling people answers, if it seems they are more interested in passing the exam than learning.

    The answer is there for you to work out, I will help you get to the answer if you are interested in learning rather than just wanting to skive through life. if you can't be arsed then you are someone who I have absolutely no iinterest in helping..

    My opinion but if someone else wants the glory then so be it. Good luck drifting through life..

    I'm out

  7. #7
    Join Date
    Jun 2008
    Location
    england
    Posts
    15
    Rep Power
    0

    Re: C.o.p question

    I agree with what you saying in principle but I find when I'm working out maths questions I learn the problem a lot better if I work backwards and can assign numbers rather than letters to an equation.


    My understanding is that in heating for ever 1kw of energy your putting in with a cop of 4 you get 4kw back.
    so a 9kw system must be using 2.25kw of energy to run it.

    In which case a 9kw system in cooling would require me to minus the energy being used 2.25kw from the 9kw which would be 6.75kw.?

  8. #8
    Join Date
    Jun 2008
    Location
    england
    Posts
    15
    Rep Power
    0

    Re: C.o.p question

    Anyone.????

  9. #9
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: C.o.p question

    Quote Originally Posted by combi99 View Post
    In which case a 9kw system in cooling would require me to minus the energy being used 2.25kw from the 9kw which would be 6.75kw.?
    Which brought you to the right answer, well done.

    The actual, real life, figure will vary slightly depending on the equipment as there are some variables and deferent way of measuring.
    However, as most of us engineers see it: cooling capacity + input power = heating capacity.

    Good luck with your studies.


  10. #10
    Join Date
    Jun 2008
    Location
    england
    Posts
    15
    Rep Power
    0

    Re: C.o.p question

    Thanks for confirming that Viking :-)